Also don't forget to drop down loop back up to prevent freeze blocks.

FM has a detail to follow I believe

Sent from my Verizon 4G LTE Droid
On Sep 18, 2016 3:23 PM, Bruce Verhei <bver...@comcast.net> wrote:
That sounds taken care of.

And Ron is correct. And the refrigerant type or N2 air dryer. And a game on 
detail project design and management. It is amazing that the number of all 
possible errors and errors you see in built systems that cause false trips 
approaches unity. Vic-type ftgs? Does designer specify cold temp gasket? Does 
purchasing agent order same gasket? Does fitter grab one from last >40f job out 
of coverall pockets? The normal mode where everyone "does their job" and 
project manager is hands off is not adequately reliable for these systems.

Best

Bruce Verhei

> On Sep 18, 2016, at 12:08, Mark Phillips <markphill...@webolton.com> wrote:
>
> Yes
> Laid uni strut on top of freezer to distribute the load then rod through the 
> freezer. Had to seal each penetration of the rod. Nut and washer on the rod.
>
> Strut was then tired into structure on either side of the unit
>
> Sent from my Verizon 4G LTE Droid
> On Sep 18, 2016 3:03 PM, Bruce Verhei <bver...@comcast.net> wrote:
> What is the structure of the freezer? Are the racks integral to that 
> structure, or free standing? Could you support system from racks?
>
> Best
>
> Bruce Verhei
>
> Go 'Hawks
>
>
>
> Sent from my iPhone
> On Sep 18, 2016, at 10:13, rongreenman . 
> <rongreen...@gmail.com<mailto:rongreen...@gmail.com>> wrote:
>
> For once we have s post where a double interlock pre action is actually the 
> proper system and our fellow forumite wants to use a single interlock. If you 
> use a SIPA you'll have ice in your pipes before a head fuses. A DIPA WONT 
> FLIW Wter into the piping until sprinklers are fused.
>
> On Sunday, September 18, 2016, 321 
> <tcf...@bellsouth.net<mailto:tcf...@bellsouth.net>> wrote:e
> I have a very large Freezer/Cooler project that I am managing. My initial 
> idea on this job has been to use a Wet Pipe System above the Freezer with 
> ESFR Dry Pendents (Class IV in rack to 20'). Due to the exorbitant cost of 
> the ESFR Dry Pendents I'm letting my thinking expand to possibly running 
> Single Interlock Pre Action inside the Freezer ...since the Freezers are 
> already up (yeah...I know !!).
>
> The ceiling panels are 6" thick and I was wondering if any of you guys in 
> your history have ever hung Fire Sprinkler Pipe inside a Freezer attaching 
> to/thru the panels and how?
>
> Thanks in advance
>
> Atlantic Realty and Building, LLC
> Palm Beach Gardens, Fl
> 561-707-5150
>
> John W. Farabee
> V.P. Fire Sprinkler Division
>
>
> --
> Sent from Gmail Mobile
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to