I am presuming the duct detectors are just inside the return air from the
cells and the day rooms  and other common areas are high ceilinged with
normal detectors or where ceilings are low the access is limited.

On Tue, Sep 20, 2016 at 7:54 AM, <craig.pr...@ch2m.com> wrote:

> Where a fire alarm system is installed, duct detectors are an initiating
> device attached to and powered by the FACP system just as any other room
> detector.  It’s essentially a regular detector head with tubes placed in
> an enclosure.
>
>
>
> Here’s a quote to chew on from the book, Operation of Fire Protection
> Systems:
>
> “The detection of duct smoke is made difficult by its dilution with return
> air from other spaces (away from the fire) and possibly with outside fresh
> air.  Also, when the HVAC system fan is not running, smoke may not reach
> the duct detector. For these reasons, air duct smoke detectors must never
> be considered as a substitute for open area protection.”
>
>
>
>
>
>
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> craig.pr...@ch2m.com
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *Parsley Consulting
> *Sent:* Tuesday, September 20, 2016 10:22 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Pre-action detection [EXTERNAL]
>
>
>
> Greg,
>     The first issue that came to my mind was that the duct detector is
> frequently provided with power from the HVAC system and not from the FACU
> or releasing panel.  I don't know the logistics of what you're dealing with
> or whether that issue might have some impact however that might be worth
> looking into.  I have to admit I'd never heard of something like this.
> That by itself doesn't mean it's outside the listing or the guidance in -72
> or -13, just that I've never run across this configuration.
>
>
> *Ken Wagoner, SET *
>
>
> *Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido, California
> 92025 *
> *Phone 760-745-6181 <760-745-6181> **Visit our website
> <http://www.parsleyconsulting.com/> *
>
> On 09/20/2016 6:28 AM, Gregg Key wrote:
>
> Greetings,
>
>
>
>                               First of all, what a great convention. Good
> speakers and fellowship. Nashville was awesome as well. I am in serious
> need of some technical assistance. I have posted this a few times with some
> response but this has become a three ring circus between the architect
> ,fire marshal and us . The Architect specified a double interlock
> pre-action system with the detection being provided with a duct detector in
> the return duct at the unit. We have refused to certify the system due the
> fact that the detector not being listed for this application. State is
> asking me to hang a partial certification ( yellow tag) . has anyone else
> dealt with this detection being used for a pre-action system in a detention
> center?   Any help would be appreciated
>
>
>
> Gregg Key
>
> General Manager
>
> Key Fire Protection Enterprises,LLC
>
> 3200 Mike Padgett Hwy
>
> Augusta GA, 30906
>
> O-706-790-3473
>
> C- 706-220-8821
>
> F- 706-738-2119
>
> gr...@keyfps.com
>
>
>
>
>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)