Or was he possibly concerned with security and tampering with the detectors in 
the cells?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Tuesday, September 20, 2016 11:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-action detection [EXTERNAL]

That's a major concern. I think the specifier saw a typical use and decided he 
could cheapen it down.

On Tue, Sep 20, 2016 at 8:14 AM, michael G 
<m...@keyfps.com<mailto:m...@keyfps.com>> wrote:
No, they are back at the main return, that is it. just one duct detector, that 
covers about 30 cell pods.   They do not have any detectors in the grilles in 
the cell pods.   that’s our main concern.

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of rongreenman .
Sent: Tuesday, September 20, 2016 11:07 AM

To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Pre-action detection

I am presuming the duct detectors are just inside the return air from the cells 
and the day rooms  and other common areas are high ceilinged with normal 
detectors or where ceilings are low the access is limited.

On Tue, Sep 20, 2016 at 7:54 AM, 
<craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> wrote:
Where a fire alarm system is installed, duct detectors are an initiating device 
attached to and powered by the FACP system just as any other room detector.  
It’s essentially a regular detector head with tubes placed in an enclosure.

Here’s a quote to chew on from the book, Operation of Fire Protection Systems:
“The detection of duct smoke is made difficult by its dilution with return air 
from other spaces (away from the fire) and possibly with outside fresh air.  
Also, when the HVAC system fan is not running, smoke may not reach the duct 
detector. For these reasons, air duct smoke detectors must never be considered 
as a substitute for open area protection.”





Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Parsley Consulting
Sent: Tuesday, September 20, 2016 10:22 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Pre-action detection [EXTERNAL]

Greg,
    The first issue that came to my mind was that the duct detector is 
frequently provided with power from the HVAC system and not from the FACU or 
releasing panel.  I don't know the logistics of what you're dealing with or 
whether that issue might have some impact however that might be worth looking 
into.  I have to admit I'd never heard of something like this.  That by itself 
doesn't mean it's outside the listing or the guidance in -72 or -13, just that 
I've never run across this configuration.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181<tel:760-745-6181>
Visit our website<http://www.parsleyconsulting.com/>
On 09/20/2016 6:28 AM, Gregg Key wrote:
Greetings,

                              First of all, what a great convention. Good 
speakers and fellowship. Nashville was awesome as well. I am in serious need of 
some technical assistance. I have posted this a few times with some response 
but this has become a three ring circus between the architect ,fire marshal and 
us . The Architect specified a double interlock pre-action system with the 
detection being provided with a duct detector in the return duct at the unit. 
We have refused to certify the system due the fact that the detector not being 
listed for this application. State is asking me to hang a partial certification 
( yellow tag) . has anyone else dealt with this detection being used for a 
pre-action system in a detention center?   Any help would be appreciated

Gregg Key
General Manager
Key Fire Protection Enterprises,LLC
3200 Mike Padgett Hwy
Augusta GA, 30906
O-706-790-3473<tel:706-790-3473>
C- 706-220-8821<tel:706-220-8821>
F- 706-738-2119<tel:706-738-2119>
gr...@keyfps.com<mailto:gr...@keyfps.com>




_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700<tel:253.576.9700>

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

________________________________
[Avast logo]<https://www.avast.com/antivirus>


This email has been checked for viruses by Avast antivirus software.
www.avast.com<https://www.avast.com/antivirus>



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)