I don't want 13 in front of me with regard to earthquakes- too complex.
My attitude, sitting here in my non-essential facility kitchen in Overland
Park, Kansas is "they are nothing to fracking worry about".
But with Oklahoma under me nowadays, I would like to see the the Fire,
Police, Hospitals, and Military Facilities people giving them a little more
thought.
On Sep 21, 2016 7:30 PM, "Bruce Verhei" <bver...@comcast.net> wrote:

> I don't have 13 in front of me. But personal experience is that pipe that
> is attached to roof, and then down to columns, racks, or (tilt-up) walls is
> subject to breaking when the ground moves. This seemed worse when
> attachment to one surface is rigid, i.e. Unistrut-type channel and clip.
> Walls and racks seemed worse than columns.
>
> I was quite shocked at how effective flex couplings were at reducing
> failures.
>
> Many breaks I saw were in auxiliary drain and inspector's test drops. 1".
> While causing property damage flow would not have caused system to fail to
> control fire. Would larger hose stream supply pipes failures cause
> inadequate flow to remain in system?
>
> Hmm. I don't know that 13 identifies a goal. Sufficient post-earthquake
> integrity to control fire? Or very few failures causing property damage?
>
> See wikipedia, Nisqually earthquake. Silty, with some layers of muck,
> soils of the Kent valley.
>
> Best
>
> Bruce Verhei
>
> Sent from my iPhone
> On Sep 21, 2016, at 10:17, Parsley Consulting <parsleyconsult...@cox.net>
> wrote:
>
> Craig,
>     The first comment is valid, if the pipe Rocci described was a "drop to
> a hose line" it would certainly require flexible couplings per 9.3.2.4.
>     I noted in Rocci's comment that he was considering an 1½", so I
> conclude that the "other piping" would not apply for lateral bracing as it
> didn't reach the 2½" minimum for branch lines and other piping.
>     As for the 4-way bracing required in 9.3.5.8, as long as the pipe
> Rocci's considering doesn't have a change in elevation of 3'-0" or more,
> there's no need for a 4-way brace.
>     And Ron's point is valid.  All system risers are "risers", however,
> not all "risers" are system risers.
>
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 <760-745-6181> Visit our website
> <http://www.parsleyconsulting.com/> *
> On 09/21/2016 10:02 AM, craig.pr...@ch2m.com wrote:
>
> You might want to look at the wording in 9.3.2.4 which deals with Flexible
> Coupling for Drops where it uses the term “drops to hose lines”.  So a
> line coming off a sprinkler system serving a hose line is referred to as a
> “drop”, not a riser.
>
>
>
> Also, for example, 9.3.5.5 speaking of lateral sway bracing uses the
> phrase “…and OTHER piping….”, therefore addressing piping in the system
> which does not fall within the definitions of Feed and Cross Mains and
> Branch lines which are the typical piping components of a sprinkler system.
> I would submit that a drop to a hose valve would fall under the “other
> piping” category.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> craig.pr...@ch2m.com
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of 
> *rongreenman
> .
> *Sent:* Wednesday, September 21, 2016 12:40 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: small hose connections [EXTERNAL]
>
>
>
> You might also want to point out for the approximately 650 lurkers on the
> forum who may be confused that a riser is any vertical piping, regardless
> of the direction of water flow that isn't a drop, sprig up or arm over
> ending with a sprig or drop.
>
> On Wednesday, September 21, 2016, Parsley Consulting <
> parsleyconsult...@cox.net> wrote:
>
> Cliff,
>     You've pointed out a conclusion on my part that was not in what Rocci
> posted.  He didn't say it was a part of a standpipe.  That was a
> supposition on my part.
>     If it were a part of a sprinkler system, such as a line feeding a hose
> valve in rack storage, the horizontal portions would not require bracing,
> in my perspective, as they simply aren't mains [longitudinal], and aren't
> branch lines [lateral].
>     Now, if they had an elevation change exceeding 3'-0", that pipe would
> be regarded as a "riser", by 3.5.9, it would require a 4-way brace at the
> top per 9.3.5.8.1.
>     It also might fall into the need for flexible couplings per
> 9.3.2.3.1(1).
>     Good call.  And I suppose I should acknowledge Craig's question, and
> note that I made the conclusion that since Rocci is in California, where
> almost everything has to be protected from earthquake damage, AND he asked
> the question, that seismic protection was necessary on his system.
> sincerely,
>
>
>
>
>
>
> *Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
> Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
> website <http://www.parsleyconsulting.com/> *
>
> On 09/21/2016 9:10 AM, Cliff Whitfield wrote:
>
> Ken,
>
>
>
> If this is an 1½” hose line in an NFPA 13 condition (which Rocci didn’t
> actually state but I’m assuming it is), then the definition of ‘branch
> line’ in NFPA 14 would not apply.  If that is the case, would this still be
> considered a ‘branch line’ or does it become a ‘feed main’?
>
>
>
> Cliff Whitfield
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *Parsley Consulting
> *Sent:* Wednesday, September 21, 2016 12:06 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: small hose connections
>
>
>
> Rocci,
>     Glad to see you made it back safely from Nashville, and it was great
> to meet there and put a face with the name.
>     By the definition in section 3.3.2 of NFPA 14 [2013 ed], the pipe you
> describe is a "branch line."  Section 6.1.2.5 of that document advises that
> you need to follow NFPA 13 to provide protection against damage from
> earthquakes.
>     Lateral bracing for that line is not required per NFPA 13 [2013]
> 9.3.5.5.1, as it is not a branch line 2½" or larger.
>     Longitudinal bracing for that line is not required per 9.5.6.1 as it
> is not a feed or cross main.
>     My opinion only.  Please see the disclaimer below.
> sincerely,
>
>
>
>
>
>
> *Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
> Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
> website <http://www.parsleyconsulting.com/> *
>
>
>
> *IMPORTANT NOTICE: This correspondence is not a Formal Interpretation
> issued pursuant to NFPA Regulations. Any opinion expressed is the personal
> opinion of the author and does not necessarily represent the official
> position of the NFPA or its Technical Committees. In addition, this
> correspondence is neither intended, nor should it be relied upon, to
> provide professional consultation or services It should be noted that the
> above is my opinion as a member of the NFPA Automatic Sprinkler System
> Hanging and Bracing Committee in accordance with the NFPA Regulations
> Governing Committee Projects and should therefore not be considered, nor
> relied upon, as the official position of the NFPA or its Committees*
>
>
> On 09/21/2016 8:17 AM, Rocci Cetani 3 wrote:
>
> Do I need to earthquake brace my 1½” feed for hose connections?
>
>
>
> *Rocci Cetani III, **CET*
>
> *Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 93037
>
> P-(408) 776-1580 EXT.111
>
> F-(408) 776-1590
>
>
>
>
>
> roc...@norcalfire.com
>
> www.norcalfire.com
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information
>
> belonging to the sender. The information is intended only for the use of
> individual or entity named above. If you are not the intended recipient, or
> the employee or agent responsible to deliver this message to the intended
> recipient, you are hereby notified that any disclosure, copying or taking
> of any action in reliance on the contents of this information is strictly
> prohibited. If you have received this transmission in error, please
> immediately notify us by telephone to arrange for return of the documents.
>
>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
> ------------------------------
>
> [image: Avast logo]
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
> Sent from Gmail Mobile
>
>
> _______________________________________________
> Sprinklerforum mailing 
> listSprinklerforum@lists.firesprinkler.orghttp://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to