AHJ won’t budge? It’s obvious to me there was no input obtained from the engine 
company. 

Carry extra stuff? Nah, already there on the engine as a preconnected hand line 
as 1.75 in. hose with 1.5 couplings. 

AHJ should’ve asked the engine company, would you rather connect two 2.5 hose 
lines to a siamese (stupid and harder to accomplish) or pull the preconnect 
hand line, remove the nozzle and connect (easy)?

Bless that AHJs heart.


Tom



> On Oct 12, 2016, at 10:26 AM, Todd Williams <fpdcdes...@gmail.com> wrote:
> 
> 
> I can see a single 2-1/2 so the trucks don't have to carry addition stuff, 
> but multiple makes no sense. 
> 
> via Newton Mail 
> <https://cloudmagic.com/k/d/mailapp?ct=pi&cv=9.1.21&pv=10.0.2&source=email_footer_2>
> On Wed, Oct 12, 2016 at 11:05 AM, Steve Leyton <st...@protectiondesign.com 
> <mailto:st...@protectiondesign.com>> wrote:
> Okay … warning to all y’all:  I’ve only had one coffee and not entirely lucid 
> yet so the following analogy may seem far-fetched.   You know how when we 
> were young and thought our parents thought and said crazy stuff?  But as we 
> get older we starting thinking and saying the EXACT SAME STUFF?   Well, let’s 
> think of industry as the kids and our AHJ’s as the parents – I find myself 
> thinking like an AHJ all the time now.    So a two way FDC is overkill?   
> Hydraulically it may well be but are we quite sure that the property 
> management company or HOA is going to diligently inspect and maintain the FDC 
> inlet?   Bugs, birds, plants, little kids stuffing things into it and 
> what-not??     No, we’re not sure which is one of the principal reasons why 
> having multiple inlets on ANY connection is a good idea, in case one is 
> damaged or encumbered.
>  
> The wet-pipe committees undertook an FDC task group between cycles to 
> determine how much water can actually be pumped into multiple 2½” inlets.  
> Coming out of that, we’re working mod’s to the prescription for how many 
> inlets should be installed based on demand.   Stay tuned for more and try to 
> see the bigger picture.
>  
> Steve L.
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Brian 
> Harris
> Sent: Wednesday, October 12, 2016 7:11 AM
> To: sprinklerforum@lists.firesprinkler.org 
> <mailto:sprinklerforum@lists.firesprinkler.org>
> Subject: RE: FDC on 13R
>  
> Overkill is exactly what I was thinking too. AHJ won’t budge so Siamese it 
> is……
>  
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com <http://bvssystemsinc.com/>
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Todd 
> Williams
> Sent: Wednesday, October 12, 2016 10:09 AM
> To: sprinklerforum@lists.firesprinkler.org 
> <mailto:sprinklerforum@lists.firesprinkler.org>
> Subject: RE: FDC on 13R
>  
> 
> I have had to do this on some 13R group homes. The AHJ wouldn't accept a 
> single 2-1/2. Seems like overkill. Two 2-1/2" connections fed from a 1500 gpm 
> pump for a 55 gpm demand. We ran 4" to the riser room and connected with a 4 
> x 1-1/4 welded outlet. 
> 
> via Newton Mail 
> <https://cloudmagic.com/k/d/mailapp?ct=pi&cv=9.1.21&pv=10.0.2&source=email_footer_2>
>  
> On Wed, Oct 12, 2016 at 9:13 AM, Brian Harris <bhar...@bvssystemsinc.com 
> <mailto:bhar...@bvssystemsinc.com>> wrote:
> Double (Siamese)
>  
>  
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com <http://bvssystemsinc.com/>
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Todd 
> Williams
> Sent: Wednesday, October 12, 2016 9:11 AM
> To: sprinklerforum@lists.firesprinkler.org 
> <mailto:sprinklerforum@lists.firesprinkler.org>
> Subject: Re: FDC on 13R
>  
> 
> Single or double?
> 
> via Newton Mail 
> <https://cloudmagic.com/k/d/mailapp?ct=pi&cv=9.1.21&pv=10.0.2&source=email_footer_2>
>  
> On Wed, Oct 12, 2016 at 8:07 AM, Brian Harris <bhar...@bvssystemsinc.com 
> <mailto:bhar...@bvssystemsinc.com>> wrote:
> Looking for opinions. AHJ wants to swap out a single 1-1/2” FDC on a 13R 
> system and replace it with a standard 2-way (2-1/2”) FDC. Thoughts, concerns, 
> suggestions, etc…..
>  
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com <http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>  
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org 
> <mailto:Sprinklerforum@lists.firesprinkler.org>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>