You cannot get all the air out of a tree system unless you can purge every
dead end. Still won't help if you have a check valve that isn't holding.
With a good check valve you will eventually get the system side up to the
highest surge the city system hits. After that the surges won't push past
the check and so no paddle movement.

On Wednesday, October 12, 2016, Mike Henke <mi...@pottersignal.com> wrote:

> Barry,
>
> Your check valve may not be holding the pressure in completely. It's
> almost impossible to remove ALL the air. So now when your pump turns on,
> water will flow into the system because of the air pockets and activate the
> VS-SP.
>
> We do not allow or recommend that the flowswitch be disassembled in the
> field. There is a specific assembly method including torque on the assembly
> screws to maintain product integrity.
>
> Yes the VSR-ST will be your least expensive option. It was designed with a
> union style coupling just for limited space applications like this.
>
> Kind Regards,
>
> mike
>
> Mike Henke CET
> Sprinkler Product Manager
> ___________________________________________________
>
>
>
> Potter Electric Signal Company, LLC
> 1609 Park 370 Place, St. Louis, MO 63042
> phone: 800-325-3936   |   direct: 314-595-6740
>
> mi...@pottersignal.com <javascript:;>   |   www.pottersignal.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org <javascript:;>] On Behalf
> Of Barry Levine
> Sent: Wednesday, October 12, 2016 9:26 AM
> To: sprinklerforum@lists.firesprinkler.org <javascript:;>
> Subject: Re: Seeking false water flow alarm suggestions
>
> I'm not on municipal water. I'm on a well, but when my 2HP pressure pump
> kicks in, it does build pressure rapidly. I had to replace all the
> sprinklers early on, due to a recall, so that probably eliminated any air
> pockets... until this latest total drain. I'm beginning to believe the only
> solution will be to buy a VSR-ST. I was hoping to be able to just get a
> VSR-S but was told I couldn't take it apart to screw it on, and as you can
> see there is no room to rotate it on the fitting without a union. Is the
> VSR-ST the most cost effective solution?
>
>
> On 10/12/2016 6:59 AM, Mike Henke wrote:
> > Barry,
> >
> > The unwanted waterflow alarms are caused by the fact that the VS-SP does
> not have a retard and you are getting water surges because you are
> connected to a municipal water supply and have some air pockets in the
> sprinkler system.
> >
> > They are called unwanted alarms, not false alarms. The device is doing
> what it is supposed to do, activate on a flow of water. The problem is
> there is supposed to be a retard to prevent the alarms caused by water
> surges.
> >
> > The solution is to replace the VS-SP with a flowswitch that has a
> retard. This would be much less expensive and much easier than trying to
> vent all air out through saddle valves.
> >
> > It is possible that if there is a check valve or BFP that can hold
> pressure in the system that the unwanted alarms will eventually stop after
> there are enough surges to build system pressure up higher than the supply
> pressure.
> > However, when you test the system, you will relieve all built up
> pressure and you'll be back into the unwanted alarm issue.
> >
> > I'm guessing you never had unwanted alarms before because it was either
> never tested or somehow there was no trapped air pockets in it to allow for
> surges.
> >
> > The data sheet for the VS-SP specifically says that it does not have a
> retard so it should not be used on systems with variable pressure water
> supplies except in cases of elevator recall. The VS-SP was designed
> specifically for elevator recall and sprinkler systems supplied by a pump &
> tank.
> >
> > Flushing the system or letting it flow through the test valve will not
> eliminate ALL the air pockets, even if the test valve is at the most remote
> location.
> >
> > Change the flowswitch to the correct one.
> >
> > Kind Regards,
> >
> > mike
> >
> > Mike Henke CET
> > Sprinkler Product Manager
> > ___________________________________________________
> >
> >
> >
> > Potter Electric Signal Company, LLC
> > 1609 Park 370 Place, St. Louis, MO 63042
> > phone: 800-325-3936   |   direct: 314-595-6740
> >
> > mi...@pottersignal.com <javascript:;>   |   www.pottersignal.com
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:sprinklerforum-boun...@lists.firesprinkler.org <javascript:;>]
> On Behalf Of
> > Barry Levine
> > Sent: Wednesday, October 12, 2016 12:01 AM
> > To: sprinklerforum@lists.firesprinkler.org <javascript:;>
> > Subject: Seeking false water flow alarm suggestions
> >
> > I drained all the water from my pipes when I installed a new water
> > filter/softener system in my home. After installing the new system,
> > which replaced some 3/4" pipe with 1" pipe in my home water system, I
> > have been getting false alarms from my Potter Electric Signal Co VS-SP
> > flow sensor. I flushed my sprinkler system using the drain and the
> > test valve, yet I believe some air pockets may still remain in my two
> > areas of coffered ceilings, where the sprinklers sit 1 foot above the
> > rest of the system. Potter recommends replacing the VS-SP with a
> > VSR-ST. I'd prefer not spending the money to replace the sensor, but
> > I'd like to hear from the professionals before I make that decision.
> > I'm thinking there may be other solutions, especially since I never
> > had any false alarms during the previous 20+ years. Possibly I could
> > attach saddle valves between each of the two sprinklers in the two
> > coffered ceilings and bleed the air out. Unfortunately, I've never had
> > any long-term luck with sad
>
>  dle valves, as they have all become inoperative over time. I've attached
> a photo of my water system in case that might be helpful. Feel free to ask
> any questions or offer any solutions. Thank you.
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org <javascript:;>
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org <javascript:;>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org <javascript:;>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>


-- 
Sent from Gmail Mobile