NFPA 13R 2010 and 2013 ED. 6.6.3 States sprinkler shall not be required in clothes, linen, and pantry closets that meet the following:

1. The area of the space does not exceed 24 square feet.

2. The least dimension does not exceed 3 feet.

3. The walls and ceilings are surfaced with noncombustible or limited combustible materials as defined by NFPA 220.


I want to say the next edition will take out #2. 



Sincerely,
Dennis Briggs, Jr. C.E.T.

On October 17, 2016 at 10:50 AM John Paulsen <j...@crwnfire.com> wrote:

Does anyone have a 2010 edition of NFPA-13R that can verify for me that there is no requirement to have sprinklers in a closet less than 24 sq. ft. even if there is a wall over 3’ long on one side? I know it’s in NFPA-13, But the later versions of 13R I have doesn’t have the verbiage for the 3’ wall and I don’t have a 13R that old to refer to. The local  jurisdiction has only adopted up to 2010.   

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 


 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
BEGIN:VCARD
VERSION:3.0
ADR;TYPE=home:;;12807 BRANDYWINE ROAD;BRANDYWINE;MARYLAND;20613;
EMAIL;TYPE=work,pref:djbri...@millerfire.com
FN:djbri...@millerfire.com
ORG:MILLER FIRE PROTECTION;
PRODID:-//Open-Xchange//7.8.1-Rev18//EN
REV:20141106T144124Z
N:BRIGGS;DENNIS;JAMES;;
TEL;TYPE=fax,work:240-823-7057
TEL;TYPE=voice,work,pref:301-736-3000
UID:764080ec-4764-4c72-bfba-4ed631b16c75
END:VCARD

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to