Thanks Travis!


From: Sprinklerforum []
On Behalf Of Travis Mack, SET
Sent: Monday, October 17, 2016 10:54 AM
Subject: Re: NFPA-13R 2010 Edition, 6.6.3


6.6.3 Except where specified in 6.6.4, sprinklers shall not be
required in clothes closets, linen closets, and pantries within
dwelling units that meet all of the following conditions:
(1) The area of the space does not exceed 24 ft2 (2.2 m2).
(2) The least dimension does not exceed 3 ft (0.91 m).
(3) The walls and ceilings are surfaced with noncombustible
or limited-combustible materials as defined by NFPA 220.


If the LEAST dimension does not exceed 3' you are good.  A closet that is
11' x 2' does not need a sprinkler.  A closet that is 4'x4' does.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
fax: 866-430-6107 <>
Send large files to us via: 

On 10/17/2016 7:50 AM, John Paulsen wrote:

Does anyone have a 2010 edition of NFPA-13R that can verify for me that
there is no requirement to have sprinklers in a closet less than 24 sq. ft.
even if there is a wall over 3' long on one side? I know it's in NFPA-13,
But the later versions of 13R I have doesn't have the verbiage for the 3'
wall and I don't have a 13R that old to refer to. The local  jurisdiction
has only adopted up to 2010.   