Sounds like an exterior floor space with no fuel load to me. The 10 ft high
noncomb ceiling is an overhang?
I'm gonna scratch my head on 8.15.7.4 a while, but I don't think that's
your get out of Sprink free card here.

Brad
On Oct 18, 2016 7:38 AM, "Dewayne Martinez" <dmarti...@total-mechanical.com>
wrote:

> NFPA 13 (07ed)8.15.7.4
>
>
>
> I have a warehouse that is 30ft tall with inset entryways with
> non-combustible walls/doors on 3 sides and open on the 4 to the outside.
> The entryway is about 10ft tall with a noncombustible ceiling.  Would
> 8.15.7.4 (or any other rule) allow me to omit sprinkler protection for
> this?  No combustibles will be stored below.
>
> Thanks,
>
> Dewayne
>
>
>