I am looking at a warehouse space that needs to upgrade from K14 ESFR to K22. 
Typically this would involve plugging the ¾” outlets and cutting in new 1” 
mechanical T’s.

I had someone ask why we could not use a ¾” brass nipple and a ¾” to 1” reducer 
to  up-size the outlet to hold a 1” head. I feel like this is not allowed, but 
I could not find specifically where. It would not really be an extension 
fitting. ¾” brass is allowed. Each change of size is done with a single piece 
reducer. The ¾” tee and nipple would be included in the calculations…

Any help on where the code addresses this setup?