Craig,

I don’t know of any requirement for the length of drops, especially in building 
that don’t require seismic restraint.  Drops to a single sprinkler are 
excluded.  The only requirement I know of is for sprigs and not drops, and in 
the commentary it specifies that it is not required on drops.
A.9.3.2.3
 (5) Within 24 in. (610 mm) of the top of drops exceeding 15 ft (4.6 m) in 
length to portions of systems supplying more than one sprinkler, regardless of 
pipe size
Drops to a single sprinkler are not required to be equipped with a flexible 
coupling because of the concern regarding the difficulty of sprinkler 
installation and replacement [see 9.3.2.3(6)]. The rotation inherent in a 
flexible coupling can prevent the development of the torque necessary to 
properly install the sprinkler.
9.3.6.6* Sprigs 4 ft (1.2 m) or longer shall be restrained against lateral 
movement.
Sprig-ups are addressed in 9.3.6.6. A vertical sprig, or a sprig-up, is 
considered the opposite of a pipe drop. A vertical sprig is a pipe rising from 
the branch line to serve an individual  upright sprinkler. They are susceptible 
to rotation during relatively minor seismic events.  The requirement for 
restraint of sprigs was originally instituted for sprigs more than 8 ft (2.4 m) 
in length but was changed in the 1996 edition of NFPA 13 to apply to sprigs 
exceeding 4 ft (1.2 m) in length. The change was based on observations of 
rotated sprigs following the Northridge, CA, earthquake. The additional 
stability gained from this requirement results in time and money saved, because 
sprigs do not have to be manually repositioned after the event. The restraint 
provisions of 9.3.6.6 do not apply to drops to individual sprinklers, because 
gravity acts to pull them back to center.

Hope this helps.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Monday, November 14, 2016 12:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Bracing on vertical sprinkler drops - 15 ft long

I’ve been hunting the answer to this question and so far have come up short.

I have a case where there are drops off the bottom of 2” branch lines down to 
sprinklers in a ceiling 15 feet below.  They are hard piped to within 2-3 ft of 
the ceiling with a flex drop from that point to the ceiling.

This is seismic design cat. B, so no EQ bracing required.

I’ve been trying to find rules on bracing of vertical drops but find only info 
on unsupported armovers, which this is not.

Also the pump rated pressure is 150 psi so the system will see pressures over 
100 psi.

Any help on locating that elusive one line or paragraph on bracing requirements 
for vertical drops would be appreciated.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>