NFPA 72 addresses curved ceilings, and I think you have done as it calls
for.

 

These are heat detector activation rules, and of course, closed sprinklers
are nothing if they are not heat detectors first :)

 

Brad

 

 

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Tim Stone
Sent: Friday, November 18, 2016 9:37 AM
To: [email protected]
Subject: Curved Roof Line

 

 

In determining the increase in design area per 11.2.3.2.4 as applied to a
curved ceiling/roof line, how do we measure the roof slope?

 

I have drawn a straight line between the peak or highest point of the curve
down to the eve and measured the slope to be 2:12. 

The straight line slope does not exceed 2:12 which would require the 30%
increase.

Due to the curve is it ok to treat this as a flat ceiling when applying the
"Slope Ceiling" criteria?

 

Thank you. 

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 