NFPA 72 addresses curved ceilings, and I think you have done as it calls for.
These are heat detector activation rules, and of course, closed sprinklers are nothing if they are not heat detectors first :) Brad _____ From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tim Stone Sent: Friday, November 18, 2016 9:37 AM To: [email protected] Subject: Curved Roof Line In determining the increase in design area per 11.2.3.2.4 as applied to a curved ceiling/roof line, how do we measure the roof slope? I have drawn a straight line between the peak or highest point of the curve down to the eve and measured the slope to be 2:12. The straight line slope does not exceed 2:12 which would require the 30% increase. Due to the curve is it ok to treat this as a flat ceiling when applying the "Slope Ceiling" criteria? Thank you. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343 <mailto:[email protected]> [email protected]