I agree that this is combustible construction with members three feet or
less on center.

Hmm, I think I see where part of my hesitation lies. I've been checking my
2013 edition instead of my 2010.
The 2013 edition changed around table 8.6.2.2.1(a) and added 'Combustible
unobstructed with no exposed members' at 225 SQFT for a hydraulically
calculated system.

I guess I'm latching onto the 'no exposed members' part, but even if you
completely stuff TJI construction with insulation, its still obstructed
construction, correct?
I read the construction definition portions of chapter 3, and I don't see
anything that would allow me to go to 225 SQFT here.

So any way I try and slice it, I'm looking at 130 SQFT, with the deflectors
1-6 below the bottom of the TJIs up to a maximum distance down of 22 from
the top of the structure.

The insulation basically does nothing except get in my way and hold mold
spores. Is that the way you guys are reading it?

On Tue, Nov 22, 2016 at 8:54 AM Greg McGahan <[email protected]> wrote:

> I agree with Travis. We have however been forced to have chicken wire or
> similar under the insulation to prevent it prematurely falling on the heads.
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>
> On Mon, Nov 21, 2016 at 5:07 PM, Travis Mack, SET <[email protected]>
> wrote:
>
> Then just do standard spray sprinklers at 130 sq ft max spacing.  Reduce
> the design area to 900 sq ft.  Use 4.2k sprinklers to keep the
> over-discharge down.  I think you are correct in using the insulation for
> your ceiling to locate your deflectors.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298480-505-9271
> fax: 866-430-6107email:[email protected]
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 11/21/2016 4:01 PM, Ben Young wrote:
>
> Travis,
>
> I actually don't want to use CC heads because of the onerous draft
> stopping requirements, so that's a negative.
> Space is heated, so we're talking wet system here.
>
>
> Benjamin Young
>
> On Mon, Nov 21, 2016 at 3:10 PM, Travis Mack, SET <[email protected]>
> wrote:
>
> I would say you have combustible framing members less than 3' on center so
> you are limited to 130 sq ft spacing.  If the space is less than 60" deep,
> you may want to consider something like the Tyco CC3 and get up to 16'
> spacing at 256 sq ft.  Also, the design area would be reduced.  You would
> have 1950 sq ft with SSU, assuming this is dry, or 1300 sq ft with CC3,
> again, assuming it is dry.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298480-505-9271
> fax: 866-430-6107email:[email protected]
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 11/21/2016 12:56 PM, Ben Young wrote:
>
> So I have a crawl space that was originally supposed to get drywall on the
> underside of the trusses, but now the owner wants sprinklers instead.
> This is inside an apartment building of type VB construction under the
> ground floor.  The crawl space is more than 36" deep, so it doesn't require
> CC heads.
> My question is how the heck do I treat the spacing for the heads I'm going
> to install?
> The structure is 14" deep TJIs that are stuffed with non-faced batt
> insulation that's held in place by furring strips.  My gut is telling me
> its not a smooth flat ceiling, but its also not exactly combustible
> obstructed either.
> At this point, I don't even know whether I should consider it obstructed
> or unobstructed.
> I'm leaning towards the insulation will act as a ceiling and I can go 1-12
> down from the bottom of the truss, and do 225 SQFT spacing, but can't find
> anything to assuage my fears in the code.
> This project was submitted under the 2010 edition of 13, but the AHJ now
> has adopted 2013, FYI.
> I looked through 8.15.1 but that doesn't really tell me HOW to space in
> these areas, just if I can omit or not... also didn't find too much of use
> in the AFSA informal interps.
> Any thoughts on this?
> Benjamin Young
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________ Sprinklerforum mailing
> list [email protected] http://lists.firesprinkler.
> org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to