16', not 17'. My error

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) via Newton Mail [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.3.29&pv=10.1.1&source=email_footer_2]
On Mon, Dec 12, 2016 at 9:59 AM, Travis Mack <tm...@mfpdesign.com> wrote:
9' + 7'-6" = 16'-6".
Your 17' dimension is too large. 2 sprinklers or 1 ex cov sprinkler.

Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 [https://www.facebook.com/pages/MFP-Design-LLC/92218417692] Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign [https://www.hightail.com/u/MFPDesign]
Sent from my iPhone
On Dec 12, 2016, at 7:46 AM, Todd Williams < fpdcdes...@gmail.com [fpdcdes...@gmail.com] > wrote:

Does the definition of small rooms include enclosed stairways? I am working on a location with 17' x 8 ft stair enclosures was wondering if I can use a single sprinkler.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) via Newton Mail [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.3.29&pv=10.1.1&source=email_footer_2]