Could you raise the pipe a few inches and use pend, or would pend work at
the elev. you are?

E=mc^2
On Jan 13, 2017 5:25 PM, "Travis Mack" <[email protected]> wrote:

> In a light or ordinary hazard area, would you be able to justify uprights
> directly on a 3" main?
>
> I have been hired to do the 3D coordination of a project designed by a
> consultant. The consultant indicated uprights directly on the 3" main.
>
> I can justify it in that the main is non-structural and this is a light
> hazard area. However, there is also the section that states you can not put
> uprights on pipe 3" and larger without a sprig or arm over that would
> comply with the 3x rule.
>
> There is no room to lower the pipe and I am semi-restricted from lateral
> movement for various other reasons.
>
> What does the collective wisdom think with this scenario? And I don't need
> formulae with a hundred exponents and variables to figure this out.
>
> Have a great weekend. Thanks in advance.
>
>