NFPA 13 (2016) Table 18.4(d) I would appreciate any and all thoughts regarding comparing item two and item four. It appears that, all other things being equal, max building height is 40 feet when using palletized portable racks but 35 feet if the racks are fixed. I know a lot of the rules are based on full scale testing, so is it just a matter that only portable were used for the 40 foot height? thanks, Brad Casterline, NICET IV Fire Protection Division FSC, Inc. P: 913-722-3473 [email protected] www.fsc-inc.com Engineering Solutions for the Built Environment