Reference NFPA #30 (2008ed)

 

Table 16.5.2.1 for non-relieving style containers for 5-60 gal containers on
single and double row racks to 20'-0"

 

So we are using 0.40/3000 plus in-racks based on layout E

 

Layout E shall mean one line of in-rack sprinklers in the flue space at
every level beginning above the first storage level above the floor and face
sprinklers at the first storage level at each upright. In-racks sprinklers
shall be spaced not more than 9 ft on centre and shall be staggered
vertically.

 

As this option is for single and double row racks, I am unsure about the
layout for the single row racks as we normally do not see face sprinklers on
single row racks. NFPA #30 does not provide any details on this option.

 

Any feedback would be appreciated.

 

 

Thank you

 

 