I believe I saved this info from this very forum but I have noted that FM
global used to have k-factors for hydrants. Here are the values:
2 3/8" 134
2 1/2" 149
2 5/8" 164

On Wed, Feb 22, 2017 at 6:48 PM, John Denhardt <[email protected]
> wrote:

> Travis - well said
>
> Brad - who really cares if hydrants have a K factor?  I know I don't.
>
> John August Denhardt, P.E.
> Strickland Fire Protection
>
> On Feb 22, 2017, at 8:45 PM, Travis Mack, SET <[email protected]> wrote:
>
> Or just use the formula in NFPA 291- Standard for Hydrant Marking and flow
> tests or something like that...
>
> Q = 29.83*d^2*Cd*P^0.5
>
> d = hydrant outlet diameter in inches
>
> C = the outlet coefficient (0.7, 0.8 or 0.9)
>
> P = Pitot pressure that is measured
>
> Not everything has to be extremely complicated and thought out to the nth
> degree.  If you are really so inclined, why not spend the next few years
> solving for Pi to the 1,000,000th point.  And guess what...... if you
> assign K to be 29.83*d^2*Cd........ you get 168 for your example.
> Wow...sometimes the simplest methods are the best.
>
> There is a true phenomenon that causes many people problems - *paralysis
> through analysis*.
>
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298480-505-9271 <(480)%20505-9271>
> fax: 866-430-6107 <(866)%20430-6107>email:[email protected]
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 2/22/2017 5:58 PM, Brad Casterline wrote:
>
> Say it's a 2.5" C=.9.
>
> I've tried to work this out a couple different ways:
> 1) a kind of long drawn out way, call it 'brad's way', and I get ~168.
> 2) a way i call the 'Bill Brooks back of napkin' way based on a few words
> he posted here a few years ago-- lightening fast, and i'll be damned if i
> dont get the same ~168! Basically, since K is the square feet area of the
> orifice he says 5*5*5.6=140, times (.9/.75) = 168.
> Anyway, if a hydrant butt has a K we could pretty quickly get the Q after
> the pitot'd P with Q=K*SQRT(P).
>
> thanks,
>
> Brad
> .
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to