Dave,
  

  
If it is a built up roof with tar and felt, it more than likely exceeds to 1000 
but/sqft limit. It is always good to do your homework.
    
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-553-3553 (tel:860-553-3553)  (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  
  

  
  
>   
> On Mar 12, 2017 at 6:47 PM,  <David Bitton 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> Steve and Todd,
>
>   
>
>   
>
>   
>
> The sentence that you quote continues with "...except  where sprinklers are 
> not required to be installed by 8.15.1.2.1 through 8.15.1.2.1 through 
> 8.15.1.2.18...".    Then, in article 8.15.1.2.1, we have "Concealed spaces of 
> noncombustible and limited-combustible construction with minimal combustible 
> loading having no access shall not require sprinkler protection."
>
>   
>
>   
>
>   
>
> The concealed space in this project meets all of these conditions, but only 
> if the roof deck qualifies as "limited-combustible construction".    So, it 
> appears to me that we do have to split hairs and determine if this assembly 
> meets the definition of limited-combustible construction.    Please note also 
> that 8.15.1.2.12 permits "exposed combustible insulation where the heat 
> content...does not exceed 1000 Btu/ft2.", so the fact that we have a 
> continuous flat surface does not by itself force us to install sprinklers.    
> The main criteria appears to be the heat content of the material, which is 
> not always easy to determine.   
>
>   
>
>   
>
>   
>
> I probably will wind up requiring sprinklers in this space, but I wanted to 
> have a specific article to back up that decision.
>
>   
>
>   
>
>   
>
> Thanks for your responses.
>
>   
>
>   
>
>   
>
> David Bitton
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Steve 
> Leyton
>   Sent:  Friday, March 10, 2017 9:07 PM
>   To:  [email protected]
>   Subject:  RE: RE: Built-up roof deck as a limited-combustible construction
>
>   
>   
>   
>
>   
>
>   
>
> I agree with Todd.    The standard says, “Concealed spaces of exposed 
> combustible construction shall be protected …”
>   
>  This trumps the subjective hair splitting with regard to what constitutes 
> limited combustible construction and to what extent combustible material 
> might be allowed in limited amounts.    You have one entire and continuous 
> surface that encapsulates the concealed space(s) in question; that’s not 
> limited, IMHO.
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> [email protected]
>   Sent:  Friday, March 10, 2017 4:07 PM
>   To:  Sprinklerforum
>   Subject:  Re: RE: Built-up roof deck as a limited-combustible construction
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> I think the term Limited Combustible is purposely vague. Personally, I would 
> think this is not limited since it covers the entire flat space and there is 
> continuity. If a fire did get into that space, it could run over the entire 
> structure with no good way for the fire department to fight it.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> What a local authority or insurance company would say is something else. You 
> probably should consult with them.
>
>   
>   
>
>
>  Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-553-3553 (tel:860-553-3553)  (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>   
>   
>
>
>   
>   
>
>   
>   
>
> On Mar 10, 2017 at 5:47 PM,  <David Bitton 
> (mailto:[email protected])>  wrote:
>
>   
>   
>   
>
> Yes, it is a flat roof, built in 1973.    I have no doubt that it will burn, 
> and I am classifying it as a combustible roof.    (I know about the fire at 
> the GM plant in Livonia.)    My question is more along the line of: Can a 
> noncombustible structure built on top of a typical built-up roof deck with 
> combustible insulation meet NFPA 13's definition of "Limited-combustible 
> construction"?
>
>   
>
>   
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Art 
> Tiroly
>   Sent:  Friday, March 10, 2017 5:14 PM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  RE: Built-up roof deck as a limited-combustible construction
>
>   
>   
>   
>
>   
>
>   
>
> Is it a flat roof?
>
>   
>
> Is it covered with gravel or stone?
>
>   
>
> If it is built of felt paper and asphalt/tar it will burn.
>
>   
>
>   
>
>   
>
> Art Tiroly
>
>   
>
> ATCO Fire Protection/Tiroly
>
>   
>
> 24400 Highland Rd CLE 44143
>
>   
>
> 216-621-8899
>
>   
>
> 216-570-7030 cell
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  David 
> Bitton
>   Sent:  Friday, March 10, 2017 4:57 PM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  Built-up roof deck as a limited-combustible construction
>
>   
>   
>   
>
>   
>
>   
>
> Hello,
>
>   
>
>   
>
>   
>
> I have a 35 ft high building being built adjacent to a 22 ft high building 
> which has a built-up, insulated metal deck roof. The structural engineer has 
> devised a sloped "snow shed" between the addition and the lower building in 
> order to distribute the increased snow load at this juncture.    This will 
> create an inaccessible concealed space on the roof which will be of 
> noncombustible construction, with the exception of its base, which will be 
> the built-up metal deck roof of the existing building.    Would you consider 
> this as meeting the definition of "limited combustible construction", meaning 
> that the space would not require sprinkler protection?
>
>   
>
>   
>
>   
>
>  David Bitton, ing./Eng.
>
>   
>   
>   
>   
>   
>
>  Quest Loss Control Services Inc.
>
>   
>
> 5100, rue de la Savane, bureau 200
>
>   
>
> Montréal, Québec
>
>   
>
> H4P 1T8
>
>   
>
>   
>
>   
>
> T: (514) 341-4545          C: (514) 996-7483
>
>   
>
>   www.questlosscontrol.com 
> (../../../../Documents/Sara's%20Important%20Stuff/HR/www.questlosscontrol.com)
>
>   
>   
>   
>   
>   
>
>   
>
>   
>
>
>
>   
>   
>   
>   
>   
>   
  
  
 