Do any members of this group have a solid background in NFPA 25 and 
inspections? I do not. I have an issue where my inspector has Red Tagged a 
riser because the results of a main drain test have weakened over the years. 
This system is over 30 years old so I do not have a system information plate to 
look at to see what the original main drain test was, but I do have some 
inspection reports dating back to January of 2014. At that time the client had 
a static of 55 and a residual of 48.

Current reading is about 70/28

Hydrant flow tests from the original calcs, last year and this year show no 
loss in city pressure.

Can anyone tell me where I should be looking for trouble? I believe the control 
valve on the private line is all the way open. The control valves on the 
backflow are open and the backflow passes inspection.

Is the only thing left an obstruction in the fire line? Could corrosion alone 
cause this issue? We put a pitot before the backflow, after the backflow and at 
the system riser. The water wasn't great anywhere. And when we opened those 
fittings we saw a fair amount of corrosion on the vertical underground pipes. 
Can we assume some corrosion on the vertical pipes means there is a lot more on 
the horizontal?

Were we correct to red tag this riser in the first place?




John Irwin - CET
Division Manager - Fire Sprinklers
Critical System Solutions, LLC
License Number: FPC16-000053
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>

[cid:[email protected]]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to