I was trying to be logical about the obstructions in the inner core discharge, 
which FM are so concerned with. Having a ‘cross’ of two 100mm wide obstructions 
seems totally untenable. 

You can’t put a Pendent ESFR over a 100mm wide bottom chord so the only 
difference with an Upright is the Range Pipe and the yoke shadow.

Cheers,

Russell Gregory

Christchurch

New Zealand

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, 28 March 2017 3:41 PM
To: [email protected]
Subject: Re: Am I reading this right?

 

If what you are saying is true, and I'm not questioning your statement, then 
this condition would not allow the lower obstruction to be the bottom chord of 
a steel bar joist or open web wood joist because the range pipe would need to 
be centered in the web of the joist and parallel to the joist, a physical 
impossibility. The obstruction would have to be something other than a 
structural member. Is this your experience?

Mark at Aero 

602 820-7894

 

Sent from my iPhone


On Mar 27, 2017, at 7:05 PM, Russell & Carol Gregory <[email protected]> 
wrote:

Because an Upright ESFR sprinkler can be connected directly to a Range Pipe of 
up to 100mm NB thus it is tested with an obstruction to core discharge. The  
Upright ESFR sprinkler must have the yoke arms aligned with the Range Pipe 
therefore the obstruction is in the shadow area from the yoke arms.

Accordingly another obstruction of up to 100mm wide may be positioned below the 
Upright ESFR, PROVIDING it is directly below the Upright  ESFR and is ALIGNED 
with the Range Pipe. If it is other than directly below and parallel with the 
Range Pipe then it is not permitted within the Core so must be at least 300mm 
away from below the Upright ESFR.

I have seen it stated that Upright ESFR are more tolerant of obstructions to 
Core Discharge but I believe this is not the case as the arrangement must be as 
I have described.

 

Regards,

Russell Gregory

Christchurch

New Zealand 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Vince Sabolik
Sent: Monday, 27 March 2017 11:53 PM
To: [email protected]
Subject: Am I reading this right?

 

NFPA 13, 2013

8.12.5.3.2.1   The requirements of 8.12.5.3.2 shall not apply
where upright sprinklers are located over the bottom chords of bar joists or 
open trusses that are 
4 in. (102 mm) maximum in width.

Does this mean that an upright ESFR can be at or near center of a bar joist?

Thanks, Vince


<image002.jpg>

11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136 
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601


Vince Sabolik 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to