You are allowed as many design basis within one system as you see fit.  Look at 
11.1.1 - A building OR PORTION THEREOF shall be permitted …..  IT does does 
design approach but even within one approach (aka area/density) you can have 
multiple design basis.


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Mar 31, 2017, at 8:22 AM, Matt Grise <[email protected]> wrote:
> 
> We are looking at a dry parking garage that has mostly flat ceilings. In one 
> small area the ceiling slopes greater than 2 in 12 as part of the ramp that 
> goes up/down. Is it acceptable to calculate one area of 2535 SF for any 
> locations that include or are next to the sloped space, but then go to the 
> flat spaces and calc 1950? I was not sure if that counted as an adjacent 
> hazard? It seems both different and similar.
>  
> The lesser operating area allows for pipe to be sized smaller thus reducing 
> dry volume and pipe cost. 
>  
> What does the forum think?
>  
> **we decided to go all 2535 sf operating area throughout the garage. On a 
> quick look, the pipe savings would not make up for the added design effort 
> (some 1.5” went to 1.25”). I thought it was an interesting question though. 
> Has anyone out there come across a similar situation?
>  
> Matt 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to