Ordinary Group 2 limits storage up to and including 12 ft.  If the storage is 
over 12 ft you have to do something else.  I will accept a shelf detail showing 
the top shelving unit.  A shelf over 10ft only allows two feet of storage 
before you exceed the 12 ft for OH-2.  What is the storage practice and items 
being stored?  You know the toy section is full of Group A plastics and needs a 
whole different look at protection.

Don't look at the occupancy look at the storage, commodity, and height to 
determine the layout.  The AHJ shouldn't be calling the occupancy anything 
other than what is defined in his code book (NFPA or IBC).  He too should be 
looking at the storage, commodity, and height of storage - all provided by you 
or the tenant.

Duane Fox, Jr.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Friday, April 07, 2017 1:10 PM
To: [email protected]
Subject: RE: Retail Building


Maybe I explained it wrong.



In the past, all Retail was labeled Mercantile, Ordinary Hazard Group II, 
unless they specifically had storage over 12' high. Pretty much all Grocery 
Stores went in OH Group II.



Now, what is stopping an AHJ from calling a Strip Mall with 13' deck and 10' 
ceilings,  "Retail Store", and requiring the design to be as per 20.3?



What am I missing?


Greg Lindholm

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, April 6, 2017 3:34 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Sprinklerforum Digest, Vol 49, Issue 3

Send Sprinklerforum mailing list submissions to
        
[email protected]<mailto:[email protected]>

To subscribe or unsubscribe via the World Wide Web, visit
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Sprinklerforum Info Page - American Fire Sprinkler 
Association<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
lists.firesprinkler.org
Your email address: Your name (optional): You may enter a privacy password 
below. This provides only mild security, but should prevent others from messing 
...




or, via email, send a message with subject or body 'help' to
        
[email protected]<mailto:[email protected]>

You can reach the person managing the list at
        
[email protected]<mailto:[email protected]>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Sprinklerforum digest..."


Today's Topics:

   1. Re: NFPA 13 dry system - residential sprinklers (Travis Mack, SET)
   2. RE: NFPA 13 dry system - residential sprinklers (Foster, Ed)
   3. RE: NFPA 13 dry system - residential sprinklers (Ed Kramer)
   4. Retail Building (Gregory Lindholm)
   5. RE: Retail Building (Bob)
   6. RE: Retail Building (Fox, Duane T. (FireMarshal))
   7. RE: Retail Building (Steve Leyton)
   8. NFPA 20 4.7.7.2  (Colin Carew (Cambridge))
   9. RE: NFPA 20 4.7.7.2 (John Irwin)
  10. RE: NFPA 20 4.7.7.2  (Prahl, Craig/GVL)
  11. RE: NFPA 20 4.7.7.2  (Tom Duross)


----------------------------------------------------------------------

Message: 1
Date: Thu, 6 Apr 2017 08:58:55 -0700
From: "Travis Mack, SET" <[email protected]<mailto:[email protected]>>
To: 
[email protected]<mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="windows-1252"; Format="flowed"

You mean I just can't pick and choose the standard edition I want to
use? :-)  I guess I am guilty of not reading the full text of the
message.  Great catch, my friend.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
MFP Design<http://www.mfpdesign.com/>
www.mfpdesign.com<http://www.mfpdesign.com>
MFP Design, LLC was started in 2001. MFP Design, LLC provides fire sprinkler 
drawings for architects, engineers and fire sprinkler contractors in the 
industry.



https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
Travis Mack | LinkedIn<https://www.linkedin.com/in/travismack>
www.linkedin.com<http://www.linkedin.com>
View Travis Mack's professional profile on LinkedIn. LinkedIn is the world's 
largest business network, helping professionals like Travis Mack discover 
inside ...




On 4/6/2017 9:01 AM, Parsley Consulting wrote:
> Remember friends that the text Travis quoted was _*added*_ in the 2010
> edition of -13.  Dewayne's inquiry began with a note that his project
> was governed by the 2007.  Still, the value for dry system water
> delivery time of 15 seconds for residential occupancies was the first
> item in Table 7.2.3.6.1.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> ***
Parsley Consulting - Founded 1985, by Donald L. Parsley 
...<http://www.parsleyconsulting.com/>
www.parsleyconsulting.com<http://www.parsleyconsulting.com>
Parsley Consulting designs and reviews residential and commercial fire 
suppression and alarm systems plans, and provides consulting services to 
authorities having ...



> On 04/06/2017 8:36 AM, Travis Mack, SET wrote:
>>
>> It can be R or I occupancy.  It doesn't matter.  It is the fact you
>> are protecting a dwelling unit with a dry pipe system.
>>
>> 7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of
>> any occupancy, the sprinklers in the dwelling unit shall have a
>> maximum water delivery time of 15 seconds to the
>> single most remote sprinkler.
>>
>> It seems like you have 15 seconds regardless.  Now, if you have a dry
>> pipe valve on the first floor and I believe you said these were on
>> the 5th floor, it seems quite unlikely you will get 15 seconds.  My
>> suggestion is to find a way to supply these sprinklers in the
>> dwelling units from a wet pipe system.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> http://www.mfpdesign.com
MFP Design<http://www.mfpdesign.com/>
www.mfpdesign.com<http://www.mfpdesign.com>
MFP Design, LLC was started in 2001. MFP Design, LLC provides fire sprinkler 
drawings for architects, engineers and fire sprinkler contractors in the 
industry.



>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Log In or Sign Up to 
View<https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
www.facebook.com<http://www.facebook.com>
See posts, photos and more on Facebook.



>> Send large files to us via:https://www.hightail.com/u/MFPDesign
>> LinkedIn:https://www.linkedin.com/in/travismack
>> On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
>>>
>>> That was one of my concerns also. R-2 floor occupancy, calculating
>>> it per light hazard but using residential heads.  If the R-2
>>> occupancy is what would dictate the 15sec delivery time then it
>>> wouldn?t matter what type of heads I used in the residential areas.
>>>
>>> *From:*Sprinklerforum
>>> [mailto:[email protected]
>>> <mailto:[email protected]>] *On Behalf
>>> Of *Travis Mack
>>> *Sent:* Thursday, April 06, 2017 8:58 AM
>>> *To:* 
>>> [email protected]<mailto:[email protected]>
>>> <mailto:[email protected]>
>>> *Subject:* Re: NFPA 13 dry system - residential sprinklers
>>>
>>> Double check delivery times. I think you need a 15 second delivery
>>> time in residential areas.
>>>
>>> Travis Mack, SET
>>>
>>> MFP Design, LLC
>>>
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>
>>> Send large files to MFP Design via:
>>>
>>> https://www.hightail.com/u/MFPDesign
>>>
>>> Sent from my iPhone
>>>
>>>
>>> On Apr 6, 2017, at 6:31 AM, Dewayne Martinez
>>> <[email protected]
<mailto:[email protected]%20%0b>>>> 
<mailto:[email protected]>> wrote:
>>>
>>>     The dry portion below the attic was laid out at max 15x15
>>>     spacing with the
>>>     lines at 15ft above the floor.  The way the rooms layout there
>>>     are long
>>>     runs with 8ft ceilings so I was going to drop down once to feed
>>>     all these
>>>     rooms with one line but I still need to size it.  This reviewer
>>>     will still
>>>     make us calculate the residential build out portion. I can get
>>>     by with a
>>>     1 1/4" line calculating  4 heads.
>>>
>>>     -----Original Message-----
>>>     From: Mark Phillips [mailto:[email protected]]
>>>     Sent: Thursday, April 06, 2017 8:17 AM
>>>     To: 
>>> [email protected]<mailto:[email protected]>
>>>     <mailto:[email protected]>
>>>     Cc: 
>>> [email protected]<mailto:[email protected]>
>>>     <mailto:[email protected]>
>>>     Subject: Re: NFPA 13 dry system - residential sprinklers
>>>
>>>     If I'm understanding
>>>     The roof system is unchanged and your adding a lower supply to
>>>     be rooms.
>>>
>>>     Use standard qr heads and same pipe sizes
>>>
>>>     The roof is still most demanding
>>>
>>>     Sent from my Verizon 4G LTE Droid
>>>     On Apr 6, 2017 9:14 AM, Dewayne Martinez
>>>     <[email protected]
<mailto:[email protected]%0b>>>>     
<mailto:[email protected]>>
>>>     wrote:
>>>     NFPA 13 (07ed)
>>>
>>>     I have an existing 5th floor shell space that is installed as a
>>>     light
>>>     hazard dry system that has pipe in the shell space and in the
>>>     attic.  They
>>>     are turning this floor into a dormitory (R-2).
>>>     1)Can I use listed residential heads on return bends and only
>>>     pick up 4
>>>     heads per 11.3.1.1 or will I need to pick up 1950SF? What if
>>>     there are
>>>     incidental areas such as a laundry room, ect. in the same areas
>>>     as the
>>>     dorm rooms?
>>>     2)What would be the required trip time be per Table 7.2.3.6.1?
>>>      15sec for
>>>     residential or 60sec for light hazard?
>>>
>>>     Thanks,
>>>     Dewayne Martinez
>>>     Fire Protection Design Manager
>>>
>>>     TOTAL Mechanical
>>>     Building Integrity
>>>     W234 N2830 Paul Rd.
>>>     Pewaukee, WI  53072
>>>     [email protected]<mailto:[email protected]>
>>>     
>>> <mailto:[email protected]><mailto:[email protected]<mailto:[email protected]%3e%3cmailto:[email protected]>>
>>>     Ph:  262-522-7110
>>>     Cell: 414-406-5208
>>>     http://www.total-mechanical.com/
>>>
>>>     [cid:[email protected]]
>>>     [cid:[email protected]]
>>>     [cid:[email protected]]  [Top Workplaces 2015]
>>>
>>>     TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
>>>     _______________________________________________
>>>     Sprinklerforum mailing list
>>>     
>>> [email protected]<mailto:[email protected]>
>>>     <mailto:[email protected]>
>>>     
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/67c723ca/attachment-0001.htm>

------------------------------

Message: 2
Date: Thu, 6 Apr 2017 16:32:30 +0000
From: "Foster, Ed" <[email protected]<mailto:[email protected]>>
To: 
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: RE: NFPA 13 dry system - residential sprinklers
Message-ID:
        
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="us-ascii"

I have appreciated the many opportunities to learn much from reading the 
exchanges on this forum.
Today I am inclined to add this comment:
"They are turning this floor into a dormitory (R-2)". I believe that the change 
of occupancy classification / use would dictate compliance with the code/ 
standards that are current to the time of change, which if I understand this 
thread is the present. The recommendation to install a wet system seems most 
appropriate.
One man's opinion.

Ed Foster
Fire Marshal
Fire Prevention Bureau
Carpinteria-Summerland Fire District
(805) 566-2451
[cid:82df1ca92855c9c2623baa3ddf8c0acda8677ac1@zimbra]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Thursday, April 06, 2017 9:02 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers

Remember friends that the text Travis quoted was added in the 2010 edition of 
-13.  Dewayne's inquiry began with a note that his project was governed by the 
2007.  Still, the value for dry system water delivery time of 15 seconds for 
residential occupancies was the first item in Table 7.2.3.6.1.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 04/06/2017 8:36 AM, Travis Mack, SET wrote:

It can be R or I occupancy.  It doesn't matter.  It is the fact you are 
protecting a dwelling unit with a dry pipe system.

7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of any 
occupancy, the sprinklers in the dwelling unit shall have a maximum water 
delivery time of 15 seconds to the
single most remote sprinkler.

It seems like you have 15 seconds regardless.  Now, if you have a dry pipe 
valve on the first floor and I believe you said these were on the 5th floor, it 
seems quite unlikely you will get 15 seconds.  My suggestion is to find a way 
to supply these sprinklers in the dwelling units from a wet pipe system.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
That was one of my concerns also. R-2 floor occupancy, calculating it per light 
hazard but using residential heads.  If the R-2 occupancy is what would dictate 
the 15sec delivery time then it wouldn't matter what type of heads I used in 
the residential areas.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>]
 On Behalf Of Travis Mack
Sent: Thursday, April 06, 2017 8:58 AM
To: 
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
Subject: Re: NFPA 13 dry system - residential sprinklers

Double check delivery times. I think you need a 15 second delivery time in 
residential areas.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 6, 2017, at 6:31 AM, Dewayne Martinez 
<[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>>
 wrote:
The dry portion below the attic was laid out at max 15x15 spacing with the
lines at 15ft above the floor.  The way the rooms layout there are long
runs with 8ft ceilings so I was going to drop down once to feed all these
rooms with one line but I still need to size it.  This reviewer will still
make us calculate the residential build out portion.  I can get by with a
1 1/4" line calculating  4 heads.

-----Original Message-----
From: Mark Phillips [mailto:[email protected]]
Sent: Thursday, April 06, 2017 8:17 AM
To: 
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
Cc: 
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
Subject: Re: NFPA 13 dry system - residential sprinklers

If I'm understanding
The roof system is unchanged and your adding a lower supply to be rooms.

Use standard qr heads and same pipe sizes

The roof is still most demanding

Sent from my Verizon 4G LTE Droid
On Apr 6, 2017 9:14 AM, Dewayne Martinez 
<[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>>
wrote:
NFPA 13 (07ed)

I have an existing 5th floor shell space that is installed as a light
hazard dry system that has pipe in the shell space and in the attic.  They
are turning this floor into a dormitory (R-2).
1)Can I use listed residential heads on return bends and only pick up 4
heads per 11.3.1.1 or will I need to pick up 1950SF?  What if there are
incidental areas such as a laundry room, ect. in the same areas as the
dorm rooms?
2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for
residential or 60sec for light hazard?

Thanks,
Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]><mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]%3e%3cmailto:[email protected]>>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]] [cid:[email protected]]
[cid:[email protected]]  [Top Workplaces 2015]

TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/5700c6e5/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 2712 bytes
Desc: image001.gif
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/5700c6e5/attachment-0001.gif>

------------------------------

Message: 3
Date: Thu, 6 Apr 2017 11:47:14 -0500
From: "Ed Kramer" <[email protected]<mailto:[email protected]>>
To: 
<[email protected]<mailto:[email protected]>>
Subject: RE: NFPA 13 dry system - residential sprinklers
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="utf-8"

A couple of things to consider:

-        Section 8.4.5.2 ? can?t use residential sprinks on a dry system unless 
specifically listed for dry systems.

-        Section 8.3.4.1(2) ? Unless the pipe is galvanized or otherwise 
corrosion resistant, minimum K-factor is 5.6.



So you?ll need a residential sprink that is listed for dry systems and is K5.6 
or greater.



Ed Kramer



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Thursday, April 06, 2017 8:13 AM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: NFPA 13 dry system - residential sprinklers



NFPA 13 (07ed)



I have an existing 5th floor shell space that is installed as a light hazard 
dry system that has pipe in the shell space and in the attic.  They are turning 
this floor into a dormitory (R-2).

1)Can I use listed residential heads on return bends and only pick up 4 heads 
per 11.3.1.1 or will I need to pick up 1950SF?  What if there are incidental 
areas such as a laundry room, ect. in the same areas as the dorm rooms?

2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for 
residential or 60sec for light hazard?



Thanks,

Dewayne Martinez

Fire Protection Design Manager



TOTAL Mechanical

Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]<mailto:[email protected]> 
<mailto:[email protected]>

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/







TOTAL Mechanical voted ?Top Workplace? for a 4th consecutive year.



-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/fd289b6d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1497 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/fd289b6d/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1694 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/fd289b6d/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1991 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/fd289b6d/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2347 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/fd289b6d/attachment-0007.jpeg>

------------------------------

Message: 4
Date: Thu, 6 Apr 2017 18:02:22 +0000
From: Gregory Lindholm <[email protected]<mailto:[email protected]>>
To: 
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: Retail Building
Message-ID:
        
<dm5pr11mb170644e888d952f01fae0338d5...@dm5pr11mb1706.namprd11.prod.outlook.com<mailto:dm5pr11mb170644e888d952f01fae0338d5...@dm5pr11mb1706.namprd11.prod.outlook.com>>

Content-Type: text/plain; charset="iso-8859-1"

Something just came up here.


What would stop someone from saying that any retail store (Small Strip Mall, 
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which calls 
for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary Hazard Group 
II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/26aa7667/attachment-0001.htm>

------------------------------

Message: 5
Date: Thu, 6 Apr 2017 12:05:11 -0600
From: "Bob" <[email protected]<mailto:[email protected]>>
To: 
<[email protected]<mailto:[email protected]>>
Subject: RE: Retail Building
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="us-ascii"

Retail vs Mercantile?



Thank you,



Bob Knight, CET III

208-318-3057



From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Retail Building



Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?



Greg Lindholm

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/cac8f112/attachment-0001.htm>

------------------------------

Message: 6
Date: Thu, 6 Apr 2017 18:10:55 +0000
From: "Fox, Duane T. (FireMarshal)" 
<[email protected]<mailto:[email protected]>>
To: "'[email protected]'" 
<[email protected]<mailto:[email protected]>>,
        "'[email protected]'"
        
<[email protected]<mailto:[email protected]>>
Subject: RE: Retail Building
Message-ID:
        
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="us-ascii"

There is no such occupancy in NFPA 101 called Retail.  They are all mercantile. 
 The difference is the height of storage on the shelving.  Group II limits the 
height of storage to 12'.  If your Mercantile has shelving storage that exceeds 
12' then 20.3 would apply.  Good luck.

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal's Office



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Thursday, April 06, 2017 2:05 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Retail Building

Retail vs Mercantile?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: 
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
Subject: Retail Building


Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall, 
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which calls 
for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary Hazard Group 
II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/2bffaf47/attachment-0001.htm>

------------------------------

Message: 7
Date: Thu, 6 Apr 2017 20:12:56 +0000
From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
To: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>,
        
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: RE: Retail Building
Message-ID:
        
<mwhpr17mb11651c417a0a435922541e84d5...@mwhpr17mb1165.namprd17.prod.outlook.com<mailto:mwhpr17mb11651c417a0a435922541e84d5...@mwhpr17mb1165.namprd17.prod.outlook.com>>

Content-Type: text/plain; charset="us-ascii"

Mercantile (Group M) is how retail is classified in the building code.   For 
our purposes Retail = Mercantile = Store = Dispensary (In Colorado, Washington 
and select other states).

Obviously there are exceptions.  Stores with racks, tire stores, other higher 
combustible-loaded "retail" uses require more robust fire protection.   But if 
you are confused about reference to an occupancy as Mercantile, it is usually 
(and that's USUALLY with emphasis) an OH2.

My opinion only,
Steve L.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Thursday, April 6, 2017 11:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Retail Building

Retail vs Mercantile?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: 
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
Subject: Retail Building


Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall, 
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which calls 
for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary Hazard Group 
II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/355a575a/attachment-0001.htm>

------------------------------

Message: 8
Date: Thu, 6 Apr 2017 20:20:33 +0000
From: "Colin Carew (Cambridge)" 
<[email protected]<mailto:[email protected]>>
To: 
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: NFPA 20 4.7.7.2
Message-ID:
        
<cy1pr07mb258890c58e0eb63d42c5b526f7...@cy1pr07mb2588.namprd07.prod.outlook.com<mailto:cy1pr07mb258890c58e0eb63d42c5b526f7...@cy1pr07mb2588.namprd07.prod.outlook.com>>

Content-Type: text/plain; charset="us-ascii"

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a 
project where the quoted fire pump comes with a Pressure relief valve and waste 
cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to get 
the flow and pressure we need to supply a freezer using LP-46 heads .  I find 
many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/9eb25937/attachment-0001.htm>

------------------------------

Message: 9
Date: Thu, 6 Apr 2017 16:27:51 -0400
From: John Irwin 
<[email protected]<mailto:[email protected]>>
To: 
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: RE: NFPA 20 4.7.7.2
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="us-ascii"

Diesel pump? Otherwise no main relief allowed.



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]<mailto:[email protected]>
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.


-------- Original message --------
From: "Colin Carew (Cambridge)" 
<[email protected]<mailto:[email protected]>>
Date: 4/6/17 4:20 PM (GMT-05:00)
To: 
[email protected]<mailto:[email protected]>
Subject: NFPA 20 4.7.7.2

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a 
project where the quoted fire pump comes with a Pressure relief valve and waste 
cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to get 
the flow and pressure we need to supply a freezer using LP-46 heads .  I find 
many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/eef42704/attachment-0001.htm>

------------------------------

Message: 10
Date: Thu, 6 Apr 2017 20:31:32 +0000
From: "Prahl, Craig/GVL" <[email protected]<mailto:[email protected]>>
To: 
"[email protected]<mailto:[email protected]>"
        
<[email protected]<mailto:[email protected]>>
Subject: RE: NFPA 20 4.7.7.2
Message-ID:
        
<bn6pr06mb3043fde56361525a52e85e75d6...@bn6pr06mb3043.namprd06.prod.outlook.com<mailto:bn6pr06mb3043fde56361525a52e85e75d6...@bn6pr06mb3043.namprd06.prod.outlook.com>>

Content-Type: text/plain; charset="us-ascii"

Is the 140 psi total pressure or pump rating?

The pressure relief valve comes into play if the combination of supply pressure 
and pump pressure exceeds the allowable system pressure, which for most cases 
is 175 psi.

So if you had fluctuating supply pressures, during a higher than normal 
pressure event, the system could relieve and not damage your downstream, 175 
psi rated system.

Is this a diesel or electric?

How much pressure do you need at these heads?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, April 06, 2017 4:21 PM
To: 
[email protected]<mailto:[email protected]>
Subject: NFPA 20 4.7.7.2 [EXTERNAL]

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a 
project where the quoted fire pump comes with a Pressure relief valve and waste 
cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to get 
the flow and pressure we need to supply a freezer using LP-46 heads .  I find 
many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/aa5da393/attachment-0001.htm>

------------------------------

Message: 11
Date: Thu, 6 Apr 2017 16:34:14 -0400
From: "Tom Duross" <[email protected]<mailto:[email protected]>>
To: 
<[email protected]<mailto:[email protected]>>
Subject: RE: NFPA 20 4.7.7.2
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="us-ascii"

Looks like you could be above 200 PSI churn or system pressure.  The
standard (2013 referenced) does not allow you to use the relief as a means
of blowing off excess pressure above 175.

Tom



Is the 140 psi total pressure or pump rating?



The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.



So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.



Is this a diesel or electric?



How much pressure do you need at these heads?




Craig L. Prahl





Hi Forum ,



Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone .



City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being

Used but 4.7.7.2 is  causing me to scratch my head .





Colin











-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170406/b8964cef/attachment.htm>

------------------------------

Subject: Digest Footer

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


------------------------------

End of Sprinklerforum Digest, Vol 49, Issue 3
*********************************************
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to