https://www.dropbox.com/s/6mts1hq4jjfkukh/wavy_vs_flat.pdf?dl=0

 

What I meant by 'wavy' as opposed to flat.

 

Brad

 

[email protected]

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Wednesday, March 29, 2017 11:22 AM
To: [email protected]
Subject: RE: 1x6 Slatted Ceiling

 

I would be skittish about that Ron because I think I understand the
reasoning behind the max 7'-6" between the beams and the max 6" below the
plane of the bottom of the beams--I think it is to make the bottom of the
ceiling jet 'wavy' as opposed to flat like you get with smooth ceiling. I've
been modeling this in my head since yesterday, so I got the talking part
done. I'll check the tenability conditions at 6'-0" A.F.F. with smooth
ceiling @ 12" deflector vs 18" deflector.

 

Brad

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Wednesday, March 29, 2017 7:49 AM
To: [email protected]
Subject: RE: 1x6 Slatted Ceiling

 

Couldn't the construction type be interpreted as "panel" or "beam and
girder"? Rooms less than 300 sqft with full height walls should facilitate
heat collection better than exposed beams. If the construction is called
panel then the deflector could be at 18" and eliminate the sprinklers above
the slats? 

 

Ron F

 

 

Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986>  for Windows
10

 

From: Brad Casterline <mailto:[email protected]> 
Sent: Wednesday, March 29, 2017 8:02 AM
To: [email protected]
Subject: RE: 1x6 Slatted Ceiling

 

Greg,

 

If this is still in the planning stage, since architects only come unglued
when you ask them to lower a ceiling, there's a good chance you could get
the slat ceiling raised about 5". You could then locate the pendent bulb in
the gap at 9'-0" A.F.F., and the bottom of the slats at 1" above the
deflector.

 

Brad



From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Tuesday, March 28, 2017 2:31 PM
To: [email protected]
Subject: 1x6 Slatted Ceiling

 

We have an office that has the grid ceiling at 10'-0", and we have a 8' x
12' area that has 1" x 6" boards as slats (The slats end up being 1x6's, 12'
long), that are about 6" apart. The top of the slats are @ 8'-8" (1'-4"
below the ceiling). This slatted area is in a 12' x 16' room.

 

I believe that we obviously have to have a normal layout of sprinklers at
the grid ceiling, but we would also have to have something below, because
the slats would break up any pattern from the ceiling level heads.

 

My 1st assumption would be a level of heads with the deflectors just below
the slats, but how would they ever activate, with no way for the heat to
collect down to them.

 

This is one that I have never run into. ????

 

Greg Lindholm 

 