Bill,

As ‘unconventional’ as this sounds, you could put another sidewall under the 
soffit instead of the pendant and have it cover the area under the soffit on 
both sides of the room.  Never done this before and it would look ‘weird’ but 
per code, it would work without adding the 3rd sprinkler in the room.

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772

[Description: New FDI Logo-4.jpg]

[email protected]<mailto:[email protected]>
www.fire-design.com<http://www.fire-design.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, May 11, 2017 3:48 PM
To: sprinklerforum <[email protected]>
Subject: Need head in soffit at far end of room?

A wise man once said, "a question well asked is a problem half solved", so I'll 
do my best.
I have a bedroom in a 13R occupancy which measures 14'x16'. There is a 24"wide 
x 18" deep soffit around the perimeter of the room. I have a residential 
horizontal sidewall head in the soffit 12" below the ceiling along the 14' wall 
and a pendent head in the soffit just below.

Here is the question: The distance from the sidewall head to the soffit at the 
far end of the room is 12'.  Since I am 6" above the bottom of the soffit, the 
minimum distance required by 8.10.7.1.3 (2010) is 13'. Do I need another head 
under the far end soffit?  It seems ridiculous, but what do you think?

Thanks much.


Bill Menster