I would write the committee for an exception for tanks only but you might not 
make it.  I think part of the reason for 3 year traditional measuring is also 
to verify the meter is accurate.  

 

 

NFPA 20, 2013 edition requires an alternate means of measuring flow when a 
metering device is installed in a loop arrangement for fire pump flow testing.  
I assume (since it doesn’t say that you don’t have to) you still need the test 
header (alternative means) if your water supply is a water storage tank??

 

I understand the reasoning behind the alternative means if you have a city 
supply because you could pump water back to suction during your test with a 
meter and it doesn’t really test the water supply.  With the meter arrangement 
you could potentially have a partially closed valve on the underground, but you 
wouldn’t necessarily know it.

 

I didn’t look it up in 25, but I believe if you have a flowmeter arrangement 
you still have to flow water through the test header every 3 years.  Just 
curious if there are multiple reasons for that requirement and if your supply 
is a tank, if it still makes sense to flow water at least every 3 years rather 
than just use a meter loop.

 

Thank you.

 

Reed Roisum

 