The characteristics of the water supply would be the same at the point of 
connection as the test hydrant assuming elevation is the same, right? The AHJ 
quoted the same section and is stating that the characteristics are not the 
same at the point of connection.

I did order the book Steve has suggested. We'll see if that sways either of our 
interpretations.

NFPA 13 (2010) - 22.4.1.5 Hydraulic calculations shall extend to the effective 
point of the water supply where the characteristics of the water supply are 
known.

TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P  320.656.0847  |  F  320.656.0312  |  E  [email protected]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Wednesday, May 17, 2017 7:31 AM
To: [email protected]
Subject: RE: Circulating Fire Main Calculations

NFPA 13, 2010, section 22.4.1.5 also states hydraulic calcs  shall extend to 
the effective point of the water supply....

It doesn't really address where that "effective point" is or should be, but it 
backs up what Steve and Travis said.


Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, May 16, 2017 5:46 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Circulating Fire Main Calculations

And to drive that home, I would refer interested users of the standards to the 
book, "Sprinkler Hydraulics" by Harold Waas, Jr.   In the chapter titled, 
"Relating Hydraulic Calculations to the Water Supply", Waas discusses and 
offers diagrams on the "effective point of a hydrant flow test".  There's a 
very helpful figure on Page 61 of the first edition.

Steve L.
Geekin' Like Cecil

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Monday, May 15, 2017 6:38 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Circulating Fire Main Calculations


As long as you have a circulating main, I just always use the point of 
connection to the circulating main as the source point.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 5/15/2017 3:17 PM, Taylor Schumacher wrote:
When calculating through the fire main supply line to the city water main in 
the street. Is it necessary to calculate back to the test hydrant if the city 
water main is a circulating main? Or, does NFPA allow calculating to the point 
where the fire line connects to the city water main?

TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P  320.656.0847  |  F  320.656.0312  |  E  
[email protected]<mailto:[email protected]>




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


________________________________
[AVG logo]<http://www.avg.com/internet-security>


This email has been checked for viruses by AVG antivirus software.
www.avg.com<http://www.avg.com/internet-security>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to