Both.  WE submitted this after trying to convince an AHJ that with a heat pump 
(aka low temp air), there was no need for separation.  It was initiated by the 
discharge diffuser but the duct itself will not be radiating a higher 
temperature so the allowance applies overall.

Apply the NFPA caveat required for committee members when writing their own 
opinions, not a formal interpretation of the NFPA or any of its technical 
committees.

Roland


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On May 31, 2017, at 5:27 AM, Zachary Siegrist <[email protected]> 
> wrote:
> 
> I have a job where the heads ( ordinary temp) are less than 1 ft 0 in from 
> the edge of a downward discharge diffuser throughout the space.  The 
> contractor has supplied me letter from the HVAC company stating that the air 
> discharged out of the diffusers are less than 100F and therefore the heads do 
> not need to be switched out or relocated to meet the specified distances in 
> Table 8.3.2.5(a).  I believe he is trying to use Item 9 under 8.3.2.5 stating 
> “ordinary temperature sprinklers located adjacent to a heating duct that 
> discharges air that is less than 100F are not required to be separated in 
> accordance with Table 8.3.2.5(a).”
>  
> My question is this:  a diffuser is listed under the heating duct category in 
> the ‘type of heat condition’ column in Table 8.3.2.5 (a).  Are diffusers 
> viewed differently than the ductwork itself?  Any thoughts as to if the 
> previously referenced section applies to sprinklers located adjacent to 
> diffusers or just sprinklers located adjacent to heating ducts?   Typically 
> heads are just switched out to intermediate temperature sprinklers but this 
> is the first time someone has taken this approach. 
> 
> Zach
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to