If there are separations that satisfy the building official, different areas within a single “building” can be protected with the two different standards. But I can’t use one standard in the dwelling units and one outside of them.
But universally, I think there’s a pretty wide-span misunderstanding of how 13R can be applied to a four-story hotel, notwithstanding corporate loss prevention standards like those of Hilton and Marriott that require more robust system design. 13R prescribes residential sprinkler design in the units and design per 13 outside of the units. 13 allows the use of residential sprinklers in corridors directly serving dwelling units, so we can say that in the upper floors of a four-story hotel, 13R design will generally prevail. If you have other uses that are mixed but associated exclusively with the hotel, you can protect them per 13 and it’s still a “13R design”. Admin, breakfast seating areas, meeting rooms, restrooms, workout and spa, housekeeping, etc. are all accessory to the principal use of the building as a hotel. So you can have a “mix” of 13 and 13R sprinkler types, areas of coverage and hydraulics, but it’s all still within the scope of 13R. Personally, I would not consider mixing the two books unless the separation you’re considering is at least two hours and is considered a fire wall per the IBC (two independent and rated assemblies). And even then I’d need a compelling reason to mix standards. We had annex language in 13R at one time that said that when the separation was considered a “building separation” you could throw both books at it but that was confusing and re-written. But let’s ask ourselves what it is: is this hotel a single building with retail stores and their associated fire loads, and/or a commercial kitchen with a statistically measurable chance of a fire originating there? Are these spaces separated from the residential ones? And if not, why be interested in downgrading protection to what is more accurately described as a mixed use building, not a dedicated hotel, i.e. residential use? We’re in the protection business – let’s sell as much of it as we can. My 2¢ only … SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Design Dept Sent: Tuesday, June 06, 2017 8:10 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Hotels Travis, Didn't they just change the IBC to allow that? Design Mgr Living Water Fire Protection, LLC 1160 McKenzie Rd. Cantonment, FL 32533 (850) 937-1850 On Tue, Jun 6, 2017 at 10:04 AM, Travis Mack <tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>> wrote: You can not have a 13 system with 13R in the units. The system is either designed per 13 or 13R, not a hybrid. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Jun 6, 2017, at 8:01 AM, Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>> wrote: It’s (4) stories, the notes on the FP drawings call for a 13 system with 13R coverage in the guest room. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Tuesday, June 06, 2017 10:40 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Hotels I do several of these every year. How tall are you talking. Are they wanting 13 or 13R? This determines a few starting factors From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: June-06-17 10:37 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Hotels Been doing this sprinkler stuff for just over 11 years now and finally ran into my first hotel project. Any tips/pointers from you guys that do a lot of these ? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989<tel:(704)%20896-9989> Fax: 704.896.1935<tel:(704)%20896-1935> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org