Do it exactly like the owner wants - with no pads -but in protest - and make 
him sign a letter that states that you recommended the housekeeping/maintenance 
pads - and he declined them.

This is an accepted engineering practice. This is how we protect the electric 
motor equipment. Good luck.

Rob Henderson
RWP Engineering  
31 W. Congress St., Suite 305
Savannah, Georgia 31401
Phone: (912) 231-9212


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, June 13, 2017 9:41 AM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 51, Issue 9

Send Sprinklerforum mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

or, via email, send a message with subject or body 'help' to
        [email protected]

You can reach the person managing the list at
        [email protected]

When replying, please edit your Subject line so it is more specific than "Re: 
Contents of Sprinklerforum digest..."


Today's Topics:

   1. RE: Pre-action detection options ([email protected])
   2. Pump pads (John Irwin)
   3. RE: Pre-action detection options (Steele, Andrew)
   4. RE: Pump pads (Mitchell, Scott)
   5. RE: Pump pads (Ed.Tambini)
   6. RE: Pump pads (Art Tiroly)
   7. RE: Pre-action detection options ([email protected])
   8. Re: Pre-action detection options (Charles Thurston)
   9. Re: Pre-action detection options (Bruce Verhei)
  10. RE: Pump pads (Dewayne Martinez)
  11. RE: Pump pads (Tom Duross)
  12. RE: Pump pads (Matthew J Willis)


----------------------------------------------------------------------

Message: 1
Date: Mon, 12 Jun 2017 12:01:54 -0400
From: [email protected]
To: Sprinklerforum <[email protected]>
Subject: RE: Pre-action detection options
Message-ID: <9eb5a2fa-08cd-450f-a06b-1a16949ae4fd@Todds-iPad>
Content-Type: text/plain; charset="utf-8"

 
 
Possibly, but would be a difficult and expensive install.
   
 
 Todd G Williams, PE
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (tel:860-535-2080)  (ofc)
 
860-553-3553 (tel:860-553-3553)  (fax)
 
860-608-4559 (tel:860-608-4559)  (cell)
 
 
 
 
 

 
 
>  
> On Jun 12, 2017 at 11:46 AM,  <Matt Grise (mailto:[email protected])>  wrote:
>  
>  
>        
>  
>
>  How about pilot line detectors with high-temp heads?
>
>  
>
>    
>
>  
>  
>
>  Matt    
>
>  
>
>    
>
>  
>  
>
>    
>
>  
>  
>  
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> [email protected]
>   Sent:  Monday, June 12, 2017 10:45 AM
>   To:  Sprinklerforum
>   Subject:  RE: Pre-action detection options
>
>  
>  
>  
>
>  
>
>  
>  
>  
>
> High temps causing device to fail.
>
>  
>  
>
>
>  Todd G Williams, PE
>
>  
>  
>
> Fire Protection Design/Consulting
>
>  
>  
>  
>
> Stonington, CT
>
>  
>  
>  
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>  
>  
>  
>
> 860-553-3553 (tel:860-553-3553)  (fax)
>
>  
>  
>  
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>  
>  
>  
>  
>  
>  
>  
>
>
>  
>  
>
>
>  
>  
>
> On Jun 12, 2017 at 11:39 AM,  <Matt Grise (mailto:[email protected])>  wrote:
>
>  
>  
>  
>
>  Are the devices activating because they sense a fire or because the high 
> temperatures cause the devices to fail?
>
>  
>
>    
>
>  
>  
>
>  Matt
>
>  
>  
>
>    
>
>  
>  
>  
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of   
> [email protected] (mailto:[email protected])
>   Sent:  Monday, June 12, 2017 10:34 AM
>   To:  Sprinkler Forum
>   Subject:  Pre-action detection options
>
>  
>  
>  
>
>  
>
>  
>  
>  
>
> I am working on a facility with a pre-action system in an industrial facility 
> with ambient ceiling temperatures in excess of 200 degreesF. They have had a 
> problem with accidental activations, mostly due to the (electronic) detection 
> system. Is there a good resource for various options for detection? The 
> standard ones are proving problematic.  
>
>  
>  
>
>
>  Todd G Williams, PE
>
>  
>  
>
> Fire Protection Design/Consulting
>
>  
>  
>  
>
> Stonington, CT
>
>  
>  
>  
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>  
>  
>  
>
> 860-553-3553 (tel:860-553-3553)  (fax)
>
>  
>  
>  
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>  
>  
>  
>  
>  
>
>  _______________________________________________ Sprinklerforum mailing list  
> [email protected] 
> (mailto:[email protected])    
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>  
>  
>  
>  
>  _______________________________________________ Sprinklerforum 
> mailing list [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>  
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/318677c9/attachment-0001.htm>

------------------------------

Message: 2
Date: Mon, 12 Jun 2017 12:11:20 -0400
From: John Irwin <[email protected]>
To: "[email protected]"
        <[email protected]>
Subject: Pump pads
Message-ID:
        <27a77db350d79043a37f2af8581140e301aeee46a...@criticalsbs.css.local>
Content-Type: text/plain; charset="utf-8"

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

What say you?



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/7bdc0f41/attachment-0001.htm>

------------------------------

Message: 3
Date: Mon, 12 Jun 2017 16:16:18 +0000
From: "Steele, Andrew" <[email protected]>
To: "'[email protected]'"
        <[email protected]>
Subject: RE: Pre-action detection options
Message-ID:
        <[email protected]>
Content-Type: text/plain; charset="utf-8"

Assuming that there is no open flame, reflected flame, or smoke associated with 
the high ceiling heat conditions, then a camera detection system, positioned in 
the building to be environmentally protected ? but still with a clear view, 
might work.   Fike Signifire is one.

Curious as to your outcome, if you would be willing to share at some point.

Andrew Steele
Fire Marshal, Dayton.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, June 12, 2017 11:34 AM
To: Sprinkler Forum
Subject: Pre-action detection options

I am working on a facility with a pre-action system in an industrial facility 
with ambient ceiling temperatures in excess of 200 degreesF. They have had a 
problem with accidental activations, mostly due to the (electronic) detection 
system. Is there a good resource for various options for detection? The 
standard ones are proving problematic.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/8d705479/attachment-0001.htm>

------------------------------

Message: 4
Date: Mon, 12 Jun 2017 16:24:47 +0000
From: "Mitchell, Scott" <[email protected]>
To: "[email protected]"
        <[email protected]>
Subject: RE: Pump pads
Message-ID:
        <[email protected]>
Content-Type: text/plain; charset="utf-8"

NFPA 20 does not explicitly require a pad.  However, proper alignment of the 
pump, driver, suction/discharge piping and requirements of 6.4 may implicitly 
require a pad.

J. Scott Mitchell, PE
Senior Fire Protection Engineer
Mission Engineering
CNS Y-12 | 865-576-5258
CNS PTX | 806-477-5883


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Monday, June 12, 2017 12:11 PM
To: [email protected]
Subject: Pump pads

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

What say you?



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]<mailto:[email protected]>
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/e1cdd1d6/attachment-0001.htm>

------------------------------

Message: 5
Date: Mon, 12 Jun 2017 16:26:07 +0000
From: Ed.Tambini <[email protected]>
To: "[email protected]"
        <[email protected]>
Subject: RE: Pump pads
Message-ID:
        
<cy4p126mb0005c77fcf66abdaa9484a60a5...@cy4p126mb0005.namp126.prod.outlook.com>
        
Content-Type: text/plain; charset="utf-8"

Isn?t there something that says the motor must be at least 12? off the floor?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mitchell, Scott
Sent: Monday, June 12, 2017 9:25 AM
To: [email protected]
Subject: RE: Pump pads

NFPA 20 does not explicitly require a pad.  However, proper alignment of the 
pump, driver, suction/discharge piping and requirements of 6.4 may implicitly 
require a pad.

J. Scott Mitchell, PE
Senior Fire Protection Engineer
Mission Engineering
CNS Y-12 | 865-576-5258
CNS PTX | 806-477-5883


From: Sprinklerforum 
[mailto:[email protected]]<mailto:[mailto:[email protected]]>
 On Behalf Of John Irwin
Sent: Monday, June 12, 2017 12:11 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Pump pads

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

What say you?



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]<mailto:[email protected]>
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/071d6400/attachment-0001.htm>

------------------------------

Message: 6
Date: Mon, 12 Jun 2017 12:36:36 -0400
From: "Art Tiroly" <[email protected]>
To: <[email protected]>
Subject: RE: Pump pads
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"

I saw it done some years ago by pipe fitters and it made me laugh.

The fittings were below the concrete floor so they gouged to floor for the 
flanges.

If you need to go back underground the ell won?t fit  at the floor.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Monday, June 12, 2017 12:11 PM
To: [email protected]
Subject: Pump pads

 

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

 

What say you?

 

 

 

John Irwin 

Division Manager - Fire Sprinklers

Critical System Solutions 

[email protected] 

813-618-2781

 

 

Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/73e8039b/attachment-0001.htm>

------------------------------

Message: 7
Date: Mon, 12 Jun 2017 12:38:39 -0400
From: [email protected]
To: Sprinklerforum <[email protected]>
Subject: RE: Pre-action detection options
Message-ID: <6466455a-943c-48c0-adf8-d72e44d1d44d@Todds-iPhone>
Content-Type: text/plain; charset="utf-8"

  
  
This is a co-generation facility and this is heat off the equipment. No flames. 
I was thinking camera or beam but I haven't worked with either before
    
  
 Todd G Williams, PE
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  
  

  
  
>   
> On Jun 12, 2017 at 12:16 PM,  <Andrew Steele 
> (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>
>  Assuming that there is no open flame, reflected flame, or smoke associated 
> with the high ceiling heat conditions, then a camera detection system, 
> positioned in the building to be environmentally protected ? but still with a 
> clear view, might work.      Fike Signifire is one.   
>
>   
>
>     
>
>   
>
>  Curious as to your outcome, if you would be willing to share at some point.
>
>   
>
>     
>
>   
>
>  Andrew Steele
>
>   
>
>  Fire Marshal, Dayton.
>
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> [email protected]
>   Sent:  Monday, June 12, 2017 11:34 AM
>   To:  Sprinkler Forum
>   Subject:  Pre-action detection options
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> I am working on a facility with a pre-action system in an industrial facility 
> with ambient ceiling temperatures in excess of 200 degreesF. They have had a 
> problem with accidental activations, mostly due to the (electronic) detection 
> system. Is there a good resource for various options for detection? The 
> standard ones are proving problematic.   
>
>   
>   
>
>
>  Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-553-3553 (tel:860-553-3553)  (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>   
>     
>   
>   
>   
>
> Web (http://www.daytonohio.gov/)      |  Twitter 
> (http://twitter.com/cityofdayton)    |       Facebook 
> (http://www.facebook.com/pages/Dayton-OH/City-of-Dayton-Ohio/47806554955)    
> |     YouTube (http://www.youtube.com/cityofdaytonohio)    |     Nixle 
> (http://www.nixle.com/)    |       E-mail Newsletters 
> (http://visitor.constantcontact.com/d.jsp?m=1101627103042&p=oi)   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>
>
>   
>       ??      _______________________________________________ Sprinklerforum 
> mailing list [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/7824c511/attachment-0001.htm>

------------------------------

Message: 8
Date: Mon, 12 Jun 2017 13:24:53 -0400
From: Charles Thurston <[email protected]>
To: [email protected], [email protected]
Subject: Re: Pre-action detection options
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"

Hello Fpdcdesign,

Look at http://www.protectowire.com/  They have a couple of lines of the cable 
listed to be installed in ambient temperatures of 200 degrees. EPC and XLR 
lines of cable. I have not used it but have worked with a little of it.

Monday, June 12, 2017, 11:34:00 AM, you wrote:


I am working on a facility with a pre-action system in an industrial facility 
with ambient ceiling temperatures in excess of 200 degreesF. They have had a 
problem with accidental activations, mostly due to the (electronic) detection 
system. Is there a good resource for various options for detection? The 
standard ones are proving problematic. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



--
Best regards,
Charles Thurston                          [email protected]
MYRTLE BEACH FIRE SAFETY GROUP
A Division of Pye-Barker Fire Safety
1445 Cannon Road
Myrtle Beach, SC 29577
(843) 916 - 8787
(843) 839 - 3473 facsimile
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/f932ff8a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 28682 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/f932ff8a/attachment-0001.jpeg>

------------------------------

Message: 9
Date: Mon, 12 Jun 2017 12:38:31 -0700
From: Bruce Verhei <[email protected]>
To: [email protected]
Subject: Re: Pre-action detection options
Message-ID: <[email protected]>
Content-Type: text/plain; charset="us-ascii"

Todd

To my knowledge the beam detectors available are not designed to be located in 
this high an ambient temperature.

Would the manufacturer allow them to operate through some type of glass, and be 
located outside the heat?

(Most techs are not really competent to install beam detectors. Most miss that 
instead of hit and miss aiming, the detectors have jacks on the front. Use a DC 
voltmeter, adjust for highest voltage, and voila, best aimed. It's amazing what 
those engineers put in the instruction docs!)

Protectowire is a quite stable product line. Again in a high temp area one 
needs to look at all the details, down to correct connections. Remote from 
panel? Some designers miss that once out of hazard area you can transition to a 
normal, conventional cable for run to panel.

For small areas you do not even need a Protectowire panel. Protectowire is 
manufactured intentionally with a higher ohms/lf than normal cable. You can use 
it as long as you stay below the ohms allowed on a normal FACP's detection 
circuits. Common is 100 ohms. Applying a safety factor a length of Protectowire 
with 80 ohms on a detection circuit is commonly used by the knowledgeable AFA 
designer.

80 ohms/0.185 ohms/lf = a typical length of detection wire acceptable on a 
releasing detection circuit.

I might encourage you to look at who would inspect final install regardless of 
panel used. Specification, design and install are not rocket science. But they 
do require following the manual, and to use all the connecting parts required. 
And they are all more expensive than normal in the van parts. 

And FM of course has discussion of linear heat detection cable for releasing 
service.

Best

Bruce Verhei 



Sent from my iPhone
> On Jun 12, 2017, at 08:34, [email protected] wrote:
> 
> I am working on a facility with a pre-action system in an industrial facility 
> with ambient ceiling temperatures in excess of 200 degreesF. They have had a 
> problem with accidental activations, mostly due to the (electronic) detection 
> system. Is there a good resource for various options for detection? The 
> standard ones are proving problematic. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/82685ae0/attachment-0001.htm>

------------------------------

Message: 10
Date: Mon, 12 Jun 2017 16:03:41 -0500
From: Dewayne Martinez <[email protected]>
To: [email protected]
Cc: [email protected]
Subject: RE: Pump pads
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"

I was taught it was a requirement of the pump manufactures for horizontal split 
case pumps.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *John Irwin
*Sent:* Monday, June 12, 2017 11:11 AM
*To:* [email protected]
*Subject:* Pump pads



We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.



What say you?







John Irwin

Division Manager - Fire Sprinklers

Critical System Solutions

[email protected]

813-618-2781





Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/97d1eac5/attachment-0001.htm>

------------------------------

Message: 11
Date: Mon, 12 Jun 2017 20:05:41 -0400
From: "Tom Duross" <[email protected]>
To: <[email protected]>
Subject: RE: Pump pads
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"

A peeve of mine.  Pads are a building code item taken out of chapter 9 and #20 
because many manufacturers are different.

Rule of thumb.  Pad is required, grouting dependent upon manufacturers base 
design.  Pad (and grout) should assume 3x the mass (weight) of driving 
equipment and extend a minimum of 6? beyond doweled anchors on all sides.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Monday, June 12, 2017 5:04 PM
To: [email protected]
Cc: [email protected]
Subject: RE: Pump pads

 

I was taught it was a requirement of the pump manufactures for horizontal split 
case pumps. 

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of John 
Irwin
Sent: Monday, June 12, 2017 11:11 AM
To: [email protected] 
<mailto:[email protected]>
Subject: Pump pads

 

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

 

What say you?

 

 

 

John Irwin 

Division Manager - Fire Sprinklers

Critical System Solutions 

[email protected] <mailto:[email protected]>  

813-618-2781

 

 

Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170612/9026e1cf/attachment-0001.htm>

------------------------------

Message: 12
Date: Tue, 13 Jun 2017 13:40:51 +0000
From: Matthew J Willis <[email protected]>
To: "[email protected]"
        <[email protected]>
Subject: RE: Pump pads
Message-ID:
        
<cy1pr19mb02048cbe7cd21c84b2fd7f06dc...@cy1pr19mb0204.namprd19.prod.outlook.com>
        
Content-Type: text/plain; charset="utf-8"

Playing DA, (Not district Attorney), If taken out of the mandating books, how 
do we make the ?other guy? do what we know is correct.

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tom Duross
Sent: Monday, June 12, 2017 6:06 PM
To: [email protected]
Subject: RE: Pump pads

A peeve of mine.  Pads are a building code item taken out of chapter 9 and #20 
because many manufacturers are different.
Rule of thumb.  Pad is required, grouting dependent upon manufacturers base 
design.  Pad (and grout) should assume 3x the mass (weight) of driving 
equipment and extend a minimum of 6? beyond doweled anchors on all sides.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Monday, June 12, 2017 5:04 PM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: RE: Pump pads

I was taught it was a requirement of the pump manufactures for horizontal split 
case pumps.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of John Irwin
Sent: Monday, June 12, 2017 11:11 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Pump pads

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

What say you?



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]<mailto:[email protected]>
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170613/013c91cc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25132 bytes
Desc: image001.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20170613/013c91cc/attachment.png>

------------------------------

Subject: Digest Footer

_______________________________________________
Sprinklerforum mailing list
[email protected]