I think you'll find that it's not required Richard, but we design for a low 
water alarm on every tank project because it's incredibly important to 
supervise the water supply.

Go online and find a company called Warrick Controls. They make liquid level 
systems using rigid electrodes and wire suspended ones, and you can custom 
arrange two or three or four or even five electrodes in a single housing to 
control pump up pump down and signaling for tanks.


Steve


-------- Original message --------
From: Richard Mote <[email protected]>
Date: 6/15/17 7:18 AM (GMT-08:00)
To: [email protected]
Subject: RE: Potter WLS

We are using the switch as a low water level alarm.
I’m starting to wonder if it is really even required. I’ve been told by several 
vendors that we are the only ones that ever buy them. Looked through the last 2 
editions of NFPA 22 and can’t find any reference to a water level switch. 
Checking the FM guides now.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  •  W: 877.324.ROWE  •  F: 570.837.6335
PO Box 407 • 7993 US Route 522, Suite 1 • Middleburg, PA 17842
RoweSprinkler.com  •  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected] or by telephone at 570-837-7647 and delete the 
message and any attachments permanently from your system.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Thursday, June 15, 2017 9:36 AM
To: [email protected]
Subject: RE: Potter WLS

How about a cla-val fill valve?

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Thursday, June 15, 2017 8:25 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Potter WLS

This is going on a bolted steel 200,000 gallon tank.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  •  W: 877.324.ROWE  •  F: 570.837.6335
PO Box 407 • 7993 US Route 522, Suite 1 • Middleburg, PA 17842
RoweSprinkler.com  •  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected]<mailto:[email protected]> or by telephone at 
570-837-7647 and delete the message and any attachments permanently from your 
system.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Thursday, June 15, 2017 9:02 AM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: RE: Potter WLS

We use a lot of buried concrete tanks up here and typically use 2 sump floats 
(one for high and one for low alarms).  The low one also operates a solenoid 
valve for the auto fill.
Dewayne

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Richard Mote
Sent: Thursday, June 15, 2017 7:33 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Potter WLS

Looking for an alternative to the Potter Electric Tank Water Level Switch. For 
whatever reason Potter has this item on backorder until the end of July. We 
have to be done and off the job by the end of June. Looking for an alternative, 
or maybe someone has one setting around they want to sell.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  •  W: 877.324.ROWE  •  F: 570.837.6335
PO Box 407 • 7993 US Route 522, Suite 1 • Middleburg, PA 17842
RoweSprinkler.com  •  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected]<mailto:[email protected]> or by telephone at 
570-837-7647 and delete the message and any attachments permanently from your 
system.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to