In situations where availability was a problem we've used the Potter PCVS 
with their PBK bracket mounted at 90 degrees.  You have to have blessing 
to do it as it's not a listed assembly in that instance, but using listed 
parts together most AHJs are fine with it.



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   John Denhardt <[email protected]>
To:     "[email protected]" 
<[email protected]>
Date:   06/22/2017 02:53 PM
Subject:        Re: Fire pump flow meter butterfly valves
Sent by:        "Sprinklerforum" 
<[email protected]>



Victaulic style 707C or the NIBCO equivalent must be used. I do not 
believe any other manufacturers make a Listed normally closed monitored 
butterfly valve. This is a NFPA 20 requirement. 

John

John August Denhardt, P.E. 
Strickland Fire Protection 

On Jun 22, 2017, at 2:34 PM, Steve Leyton <[email protected]> 
wrote:

Are you asking about valves that are described in a tech data sheet as a 
“normally closed butterfly valve”?   Like in Nibco’s catalogue, you have 
to order the N suffix or something like that?  Assuming yes, all that 
means is that it’s a regular, everyday fire protection butterfly valve but 
the tamper switch kit is factory-wired for NC service.   So if your 
question is about the tamper switch, yes you want normally closed ones for 
a flow meter/test bypass.
 
I think.
 
SL
 
From: Sprinklerforum [
mailto:[email protected]] On Behalf Of Mark 
Phillips
Sent: Thursday, June 22, 2017 11:16 AM
To: '[email protected]'
Subject: Fire pump flow meter butterfly valves
 
I keep going back and forth on the answer so I am asking for help
 
Does the flowmeter bypass butterfly valves have to be normally closed 
monitored valves? Or can they be just be monitored butterfly valves.
Thanks in advance
 
 
Mark 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=B_Z_t7nRaI2u5z2daFABhZGVBfY7Tv3Tyg_pmU946U4&s=UFxy1F-Wmxp8JcPorfQXN82RhALVGDFXU5khOYvCr6U&e=
 




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to