Is this a fire wall that splits one structure? I assume when you say ‘top of the wall’ there is a roof/ceiling up there?
Have you thought about an automatic fire door? I see those a lot in warehouses. Matt From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, July 20, 2017 2:50 PM To: Sprinklerforum Subject: Sprinklers protecting openings I may have referenced this before, but now this is turning into a job, so i need to get serious. Two 8x8 openings in a 18 ft high wall separating 2 buildings. FM and insurance company want water curtain on each side of the wall. The top of the wall is 10 ft above the openings. My thought was to run a "shelf" 18" above the top if the opening and put sprinklers spaced at 6'-0" below it. My question is how far out the shelf should project from the wall? I was thinking 2-3 ft but not sure if there is an guidance or experience with this. Thoughts? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-553-3553<tel:860-553-3553> (fax) 860-608-4559<tel:860-608-4559> (cell)