I've seen ordinary temp fusible link heads operate over second floor build out 
offices in 24' nominal clear space tilt-ups. This has been during what passes 
for hot weather in central Puget Sound. I can't confirm 165 or 175f. 

I've seen this in both enclosed above ceiling area, and in areas with 4-5' 
opening to warehouse on two sides at perimeter of new offices. 

The classic set up is buildout that occurs some time after the original shell 
construction. 

My experience is this tends to not happen during first year, but after a number 
of summers.

Best

Bruce Verhei 

> On Aug 8, 2017, at 20:10, Top Myers <t...@myersrisk.com> wrote:
> 
> I believe NFPA-13 changed to 200-degree attic heads because the response time 
> between 165 and 200 was very small and there have been more than a few 
> sprinklers in attics that have activated with and without vents. Sprinkler 
> heads that activate when there is no fire hurts all of us.
>  
> Top Myers
>  
> Myers Risk Services
> 2102 Kimberton Road, Unit 741
> Kimberton, PA 19442
> (484) 924-8155   Cell 610-952-0965
> t...@myersrisk.com
>  
> Providing Solutions For Your Risk Management Needs
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Travis Mack; MFP Design, LLC
> Sent: Tuesday, August 8, 2017 4:19 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: 175 degree sprinks in attic.
>  
> We had this issue in AZ with the interstitial sprinklers.  They were only 
> rated at 175F.  That is a problem in Arizona attics.  They have now come out 
> with 200F sprinklers.  I questioned one of the manufacturers at one time and 
> they referred me back to the chart in NFPA 13 that says you must use 
> intermediate temp and they said that the 175 was fine.  However, there was 
> little response when I said the 50F above ambient temp.  Attics in AZ get 
> above 125F without much trouble.
>  
> So, to your question, I believe there were some stories of activations due to 
> excess temps.  Depending on your location and temperatures, it may not be as 
> much of an issue.
>  
> Travis Mack, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:tm...@mfpdesign.com
>  
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>  
> **PLEASE NOTE NEW ADDRESS**
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Scott Futrell
> Sent: Tuesday, August 8, 2017 1:16 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: 175 degree sprinks in attic.
>  
> Todd,
>  
> Glass bulb or fusible link?
> I’ve documented 155°F and 165°F sprinklers operating in attics, but I don’t 
> think I’ve seen a 175°F.
> I’ve also documented fusible link, ordinary temperature-rated sprinklers 
> operating in unconditioned attics.
> I’m aware that not all attic sprinkler op’s are reported or documented though.
>  
> Scott
>  
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of fpdcdes...@gmail.com
> Sent: Tuesday, August 08, 2017 3:05 PM
> To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
> Subject: 175 degree sprinks in attic.
>  
> Has anyone know of any issues with 175 degree sprinklers in an unheated attic 
> space instead of 200 degree?
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org