By definition, a "Branch Line" is piping that connects a single hose connection 
to a standpipe.  Per NFPA 14, §7.6.3, branch piping shall be based on the 
hydraulic criteria of §7.8 but not smaller than 2½".  Since you're at the base 
of a standpipe and not near the presumed remote area, I'd say it's likely that 
2½" is adequate.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Rocci Cetani 3
Sent: Wednesday, August 09, 2017 8:24 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: standpipes

I have a situation where my 6" standpipe is coming into stairwell @  16' AFF 
can I drop down 11' (to get to my max 5 AFF)  with 2.5" to feed the hose valve 
on the 1st floor or does it need to drop down  6" with a 2.5" outlet?


Thanks in advance Mr. Leyton for your assistance :)

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to