In a prior life, the folks at Hilti have provided me ‘Engineered Judgements’ 
for installations that don’t fully comply with the UL listing.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Gary Stites
Sent: 2017/08/10 11:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Wall penetrations

Eddy flow told me to contact the firestop companies. I would think this would 
have come up before now.

Quote:
"We do not perform any fire penetration tests on our sprinkler pipe.    
Engineered Pipe (FLOW) has been manufactured for over 25 years.   I would think 
3M or others would have a fire rated penetration tested thru UL.   They have 
these details for electrical conduit/PVC Pipe which is a thinner wall thickness 
than a Flow sprinkler pipe.     Please check with your fire stop manufacturer 
for their recommendations."

All the details I have looked at are, as bullmoose said, they are OK with EMT, 
PVC, Copper etc. But steel pipe has to be "Sch.10 (or heavier)"

On Thu, Aug 10, 2017 at 7:39 AM, Roland Huggins 
<rhugg...@firesprinkler.org<mailto:rhugg...@firesprinkler.org>> wrote:
Did you contact Eddy Flow since they have a vested interest?



Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org<http://www.firesprinkler.org/>



Fire Sprinklers Saves Lives



From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Gary Stites
Sent: Wednesday, August 09, 2017 4:18 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Wall penetrations

Hello Forumites!

I'm penetrating some walls with listed thinwall pipe (Eddy Flow). All of the 
firestop details from Hilti or 3M say the penetrant shall be "Sch.10 or 
heavier". Is their a detail for listed thinwall? Do I have to upsize to Sch.10 
at the wall to penetrate it?

Thanks guys...
--
Gary Stites
805-769-GMAN
​www.sprinklersoft.com<http://www.sprinklersoft.com/>

RLH<http://www.rlhfp.com/>
WWW.K25.Rocks<http://www.k25.rocks/>
Pandora Station<http://www.pandora.com/?sc=sh43464983213902734>


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Gary Stites
805-769-GMAN

RLH<http://www.rlhfp.com/>
WWW.K25.Rocks<http://www.k25.rocks/>
Pandora Station<http://www.pandora.com/?sc=sh43464983213902734>

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Gary Stites
805-769-GMAN

RLH<http://www.rlhfp.com>
WWW.K25.Rocks<http://WWW.K25.Rocks>
Pandora Station<http://www.pandora.com/?sc=sh43464983213902734>

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to