As I understand - the control valve is so you can shut down the individual 
system for maintenance. The check valve is so you don't have to shut them all 
down in order to drain the standpipe (and risk leaving a valve closed).

The NFPA 13 annex has a couple of diagrams indicating suggested layouts. The 
location of the pressure reducing valve depends on how much water pressure the 
fire department wants at the hose connection. If the FD wants the pressure 
limited at the hose connection, then put it before. If the FD does not mind or 
prefers extra pressure, then put it after.

Be sure to check NFPA 14 requirements regarding PRV's that serve hose 
connections.

Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Wednesday, August 30, 2017 4:10 PM
To: [email protected]
Subject: NFPA 13 8.17.5.2.2(1)


Wondering ,  what is reason behind the Control valve and check valve of the 
same size at the connection is required per 13 8.17.5.2.2 (1)


I have a connection , where I connect to the standpipe  with 2.5" pipe and then 
 to a PRV control valve , then after I feed a standard hose valve and reduce 
down to 2" for my sprinkler control valve assembly .


Thanks .


Colin Carew