You would use the 16'x16' once you go over the 14' mark

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Friday, September 22, 2017 9:08 AM
To: [email protected]
Subject: Spacing EC heads per FM 3-26

 

I have a job where I'm using EC heads per FM 3-26 table 2 in a HC-3 hazard.

 

When calc'n EC normally I've always used the design criteria recommendations
per the cut sheet (ex. for 14x14 spacing use this psi / gpm etc.)

 

But in this this situation would it be recommend to stick to the 14x14 or
16x16 spacing, or could I use the demand requirements for how the head is
space, say 15x15?

 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 