I have been required to have the “flutes” packed with mineral wool in order to 
use panel construction in circumstances like you indicate.

 

We have used beam and girder without the packing when the spacing permits.

 

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Monday, October 9, 2017 3:16 PM
To: [email protected]
Subject: Obstructed Construction Clarification

 

Sorry in advance if this has already been addressed ad nauseam.

 

It’s pretty common to see steel beam construction with concrete over a 
corrugated metal deck (see Exhibit 3.32 in the 2016 handbook for a picture). 
This kind of construction can fall into three categories (correct me if I’m 
wrong):

 

1.      Unobstructed
2.      Obstructed – Beam and Girder Construction, when the beams are spaced 3 
ft. to 7.5 ft. on center
3.      Obstructed – Panel Construction, when the beams are spaced more than 
7.5 ft. on center when the area of each panel is limited to 300 S.F.

 

Now, for Panel Construction, there is some wording that states “there should be 
no unfilled penetrations in the cross-sectional area of the bounding structural 
members including the interface at the roof”. This wording is not included in 
the definition of Beam and Girder Construction. So my question is:

 

Do the spaces between the top of the beam and the deck that are typical to this 
type of obstruction preclude you from defining it as Panel Construction? 
Further, since the wording about unfilled penetrations is absent from the 
definition for Beam and Girder Construction, can I call it obstructed 
construction in areas where the beams are close than 7.5 ft. on center, even 
with these openings?

 

[NOTE: In this scenario there is no fireproofing filling the voids between the 
roof deck and the tops of the beams.]

 

Thanks.

 

-Kyle M