You are correct Ron.
*From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *rongreenman . *Sent:* Tuesday, October 17, 2017 3:09 PM *To:* [email protected] *Subject:* Re: Electric unit heaters If the heaters were to start a fire what would be the fuel source? What would actually be on fire? From the description I’m guessing the only combustible would be the insulation on the units’ wiring. On Tue, Oct 17, 2017 at 12:51 PM Dewayne Martinez < [email protected]> wrote: NFPA 13 07ed Noncombustible parking garage where they are adding a non-combustible ceiling and 3 electric unit heaters above the ceiling to keep this space warm for plumbing drain pipes. Do I need sprinkler protection in the space above the ceiling? My instinct tells me yes, at least local protection by the UH’s but I can’t find it in NFPA 13. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 [email protected] Ph: 262-522-7110 Cell: 414-406-5208 *http://www.total-mechanical.com/ <http://www.total-mechanical.com/>* [image: Consecutive Honors 2012-2017] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Sent from Gmail Mobile