You are correct Ron.


*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *rongreenman .
*Sent:* Tuesday, October 17, 2017 3:09 PM
*To:* [email protected]
*Subject:* Re: Electric unit heaters



If the heaters were to start a fire what would be the fuel source? What
would actually be on fire? From the description I’m guessing the only
combustible would be the insulation on the units’ wiring.



On Tue, Oct 17, 2017 at 12:51 PM Dewayne Martinez <
[email protected]> wrote:

NFPA 13 07ed



Noncombustible parking garage where they are adding a non-combustible
ceiling and 3 electric unit heaters above the ceiling to keep this space
warm for plumbing drain pipes.  Do I need sprinkler protection in the space
above the ceiling?  My instinct tells me yes, at least local protection by
the UH’s but I can’t find it in NFPA 13.

Thanks,



Dewayne Martinez

Fire Protection Design Manager



*TOTAL Mechanical*

*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

*http://www.total-mechanical.com/ <http://www.total-mechanical.com/>*