Craig I was specifically referring to the seal on the back or dirty side of
the lid. I'm on my phone right now so can't type a wall of text for you,
but if you're interested tomorrow I'll be happy to expound.

On Wed, Oct 18, 2017 at 5:12 PM Prahl, Craig/GVL <[email protected]>
wrote:

> The TYCO Royal Flush does speak of air flow around the plate in one
> section of the data sheet but it also shows a positive seal between the
> plate and ceiling when you purchase the gasketed cover. It’s detailed in
> the data sheet.
>
>
>
> Viking’s cleanroom sprinkler cover assembly also has a built-in gasket to
> provide a positive seal.
>
>
>
> You can’t have it both ways, a positive seal and free flow of air through
> the sprinkler between the cleanroom and ceiling space.
>
>
>
> If you have airflow through the sprinkler you will not achieve certain
> level of cGMP, FDA or ISO standards.  But like stated before, the term
> Cleanroom covers a broad array of hygiene so in some cases a simple
> concealed sprinkler is more than adequate but in other cases a concealed
> sprinkler alone would not provide adequate infiltration protection.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Ben Young
> *Sent:* Wednesday, October 18, 2017 5:00 PM
> *To:* [email protected]
> *Subject:* Re: Clean Room Sprinkler Options [EXTERNAL]
>
>
>
> The listing of the concealed sprinkler requires airflow out the top of the
> clean room lid. I'm going through this now on a project and you cannot seal
> both sides. If you check with any concealed sprinkler manufacturer they
> will tell you that airflow out the top of the cup is required.
>
>
>
> On Wed, Oct 18, 2017 at 4:31 PM Prahl, Craig/GVL <[email protected]>
> wrote:
>
> The cover is held on by solder tabs which melt and release the cover when
> the setpoint temperature of the cover plate is reached.
>
>
>
> You can also purchase a dust and air seal to prevent air and dust from
> passing through the cover plate.
>
>
>
>
>
>
>
>
>
> *Craig L. Prahl *Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Mark
> Sornsin [FAR]
> *Sent:* Wednesday, October 18, 2017 4:17 PM
> *To:* '[email protected]' <
> [email protected]>
>
>
> *Subject:* RE: Clean Room Sprinkler Options [EXTERNAL]
>
>
>
> I would also argue that unless the manufacturer declares that the ‘holes
> in the cup’ cannot be covered, then there may not really be an issue with
> regard to increased response time (even if the response actually equates
> more with SR).
>
>
>
> Moreover, this is a clean room. If the sprinklers are activating it’s too
> late for the material/equipment in the clean room – they are providing
> life-safety benefits and controlling a fire to prevent spread to other
> parts of the building.  Does it REALLY matter if it is QR or SR?
>
>
>
>
>
> [image: Visit our Website at www.SummitCoUS.com]
> <http://www.SummitCoUS.com>
>
> *Mark* *Sornsin*
> Sr. Fire Protection Engineer
> Direct: 701-499-1391
> Cell: 701-526-8585
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Prahl,
> Craig/GVL
> *Sent:* Wednesday, October 18, 2017 7:26 AM
> *To:* [email protected]
> *Subject:* RE: Clean Room Sprinkler Options
>
>
>
> Cleanrooms come in various classifications.  In some cases, you cannot
> have a standard pendent sprinkler as it would create surfaces where dust
> and other foreign material could collect and would also be difficult to
> clean.
>
>
>
> There is not a perfect sprinkler solution for cleanroom spaces but when
> you are dealing with pharmaceutical, food, or other consumable and/or
> regulated materials, the rules for hygiene restrict you from using the same
> sprinkler you might use at the grocery store.
>
>
>
>
>
>
>
>
>
> *Craig L. Prahl *Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Larry
> Keeping
> *Sent:* Tuesday, October 17, 2017 11:55 PM
> *To:* [email protected]
> *Subject:* RE: Clean Room Sprinkler Options [EXTERNAL]
>
>
>
> I’m no expert on clean rooms or concealed sprinkler’s etc. and while  I
> think the dry sprinkler with the boot is an interesting concept, but I
> don’t think it is meant for that type of application. The brochure for the
> boot says it is intended predominantly for use with clearance holes through
> freezer ceiling structures.
>
>
>
> I would advise against using any concealed (or recessed) type sprinklers
> in a clean room, because they are all vented. I understand this is because
> the heat from the fire is supposed to flow through the vents up into the
> ceiling space. Concealed sprinklers have that gap for the cover plate as
> part of the venting configuration.
>
>
>
> Even the Reliable “sealing” concealed sprinkler, which seals off the cover
> plate gap is not allowed in ceilings which have positive pressure.
>
>
>
> I’ve been told that the reason FM doesn’t sanction Q/R concealed
> sprinklers is because their testing has found that a Q/R concealed
> sprinkler’s sensitivity is roughly equal to a standard response sprinkler
> installed 12 inches below the ceiling. With this, if you interfere with
> sprinkler’s ability to vent up into the ceiling space, as with a boot tight
> to the cup (ie. with no clearance hole) or with insulation all around the
> sprinkler, you must be even more seriously degrading the sensitivity.
>
>
>
> If it was up to me I’d use a standard pendant sprinkler in clean room
> applications.
>
>
>
> Way-back-when, I did some work at Litton systems and they had a special
> custom fitting/escutcheon with a gasket to make a tight connection to the
> ceiling, so nothing could transfer from the concealed space into the clean
> room.
>
>
>
> Larry Keeping
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Prahl,
> Craig/GVL
> *Sent:* October-17-17 4:17 PM
> *To:* [email protected]
> *Subject:* RE: Clean Room Sprinkler Options
>
>
>
> If you have a LH or OH criteria where the concealed heads can be used, one
> method that was approved by one of the big insurers for a similar
> installation used the TYCO DSB-2 dry sprinkler boot on the sprinkler drop.
> The boot was placed over the drop and sealed against the upper side of the
> celling panel.  The concealed sprinkler used the gasket option on the room
> side of the sprinkler.
>
>
>
> This method according to the underwriter had been proven to stop any
> infiltration into the occupied space from the ceiling cavity.
>
>
>
> But if you have an EH occupancy, then that’s another story.
>
>
>
> I would highly recommend contacting the owner’s Risk Consultant or
> Insurance Underwriter or EOR for input or approval on any method proposed.
>
>
>
> Since this could be a “H” occupancy I do certainly hope there is a
> qualified engineer involved in the project.
>
>
>
>
>
> *Craig L. Prahl *Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Larrimer,
> Peter A
> *Sent:* Tuesday, October 17, 2017 3:16 PM
> *To:* [email protected]
> *Subject:* Clean Room Sprinkler Options [EXTERNAL]
>
>
>
> Can anyone please assist with a recommendation for a “clean room”
> sprinkler where the clean rooms are designed to be negative pressure (for
> compounding dangerous drugs).
>
>
>
> The concealed sprinkler cut sheets that I’ve looked at online generally
> say that the concealed heads cannot be used in negative pressure rooms
> (positive pressure plenums) and this is the type of room design that we
> require.  The FlexHead cleanroom ceiling sprinkler connection doesn’t
> appear to be easy to clean after installation.
>
>
>
> What type of quick response sprinkler could be used in a negative pressure
> room that is readily and easily cleanable?  Users wanted to used concealed
> sprinklers as they thought that the concealed sprinklers would be easy to
> wipe down when necessary, but we don’t want to violate the installation
> instructions on the cut sheets that state that the concealed sprinklers
> can’t be used with positive pressure plenums (negative pressure rooms).
>
>
>
> Thanks in advance.
>
>
>
> Pete Larrimer
>
> VA
>
>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> --
>
>
> Benjamin Young
> _______________________________________________
> Sprinklerforum mailing list