Trapeze to spread the load?




Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:33 PM
To: [email protected]
Subject: RE: lag bolts



Sorry I should have clarified, this is for hangers not EQ bracing



Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





[email protected]

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.



From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mitchell, Scott
Sent: Wednesday, October 25, 2017 10:24 AM
To: [email protected]
Subject: RE: lag bolts



Through bolt?



J. Scott Mitchell, PE

Senior Fire Protection Engineer

Mission Engineering

CNS Y-12 | 865-576-5258

CNS PTX | 806-477-5883

thMYA3SSEP





From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:21 PM
To: [email protected]
Subject: lag bolts



NFPA 13 9.1.5.3.2 states that if 2½” long screws can’t be used then 2” can
but spacing can’t exceed 10’….what’s one to do if 3” lags can’t be used? We
have a 6” main and only 2½” x 12” wood joists to attach to.



Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





[email protected]

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to