I’d also look at the install manual for the head you’re selecting.

Best 

Bruce Verhei 

> On Nov 8, 2017, at 14:59, Jerry Van Kolken <[email protected]> wrote:
> 
> I have a project with Group A plastic storage, We are installing ESFR 
> sprinkler to protect the storage per Table 17.2.3.1 (2013). I just found out 
> a bunch of radiant heats are going to be installed in the area, and I might 
> need to up the temp of the ESFR. Is there a temp. requirement for the ESFR 
> similar to the curves in chapter 16-2.1.3.2? I’ve gone through chapter 17 and 
> can’t find it, so I wanted to confirm I didn’t miss it.
>  
> Thanks
>  
> Jerry Van Kolken
> Millennium Fire Protection Corp.
> 2950 San Luis Rey Rd.
> Oceanside, CA 92058
> (760) 722-2722 FX 722-2730
>  