Does the standard define the standpipe as a post or pylon?

On Tue, Nov 14, 2017 at 12:10 PM Mike B Morey <[email protected]> wrote:

> Where is the standpipe located?  Are we talking a typical stairwell
> install or elsewhere?  Section 307 starts off by stating that it governs
> circulation paths, and stairs aren't part of that definition in section
> 1005 based on a quick look.  The standard is available several places
> online if you google it, not sure if they're "legal" copies but for the
> sake of answering the question I'd take a look at that angle.  If its in a
> hall or something I'd imagine it could be put in a box in the wall or
> something.
>
> ------------------------------
>
> *Mike Morey*
> *CFPS 3229 • NICET S.E.T. 123677*
> *Project Manager* • Fire Protection Group
> * Shambaugh & Son, LP **an EMCOR Company*
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> * email *[email protected]
>
>
>
>
>
>
>
> From:        James Litvak <[email protected]>
> To:        "[email protected]" <
> [email protected]>
> Date:        11/14/2017 02:59 PM
> Subject:        ANSI A1171.1 Figure 307.3
> Sent by:        "Sprinklerforum" <
> [email protected]>
> ------------------------------
>
>
>
> I'm working on building permit plans for a job, and the architect passed
> on an email from their accessibility consultant that the fire department
> hose valves can't protrude beyond the standpipe riser more than 4", per
> ANSI A117.1 figure 307.3. The text of that section is:
>
> 307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted
> to overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm)
> and not more than 80 inches (2030 mm) above the floor. Objects on multiple
> posts or pylons where the clear distance between the posts or pylons is
> greater than 12 inches (305 mm) shall have the lowest edge of such object
> either 27 inches (685 mm) maximum or 80 inches (2030 mm) minimum above the
> floor.
>
> What they're saying is that we will need to turn an elbow up from the
> outlet of the standpipe and install the valve vertical. I've already told
> them this won't work anyway, since the valve itself has a 5" hand wheel,
> and due to takeouts, the least amount of projection physically possible is
> about 8". According to the consultant, the way to mitigate this is to
> install cane protection, which the architect appears to want to avoid. Is
> anyone aware of this code section, and does it apply the way I'm being told
> it does? In nearly 13 years as a designer, I've never been told such a
> requirement exists.
>
>
> James
> Charlotte, NC_______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=wiCt1iqr5u69Txm-iBELel0Xzd3F5uGuCJUQXBz1wqg&s=xRsf5UToNzmQSkkENHTI-JrcpESCaLYKnTi-kcXYGmg&e=
>
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 
Sent from Gmail Mobile