Brad,

Perhaps a better look at the form is in order.

The form template can be used for either longitudinal or lateral seismic bracing.

Should the form be used for calculating the longitudinal bracing Fpw the limitations in 9.3.5.5.2 do not apply.  The clarification of this is provided in the text of the section which notes, in part, "_*Lateral*_ sway bracing shall be in accordance with either Table 9.3.5.5.2(a) through Table 9.3.5.5.2(l)..."

As I am a member of the hanging and bracing committee please see the disclaimer below.

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***

*IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services**
**
**It should be noted that the above is my opinion as a member of the NFPA Automatic Sprinkler System Hanging and Bracing Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees*




On 11/27/2017 9:15 AM, [email protected] wrote:
Please refer to NFPA 13 (2016).

Figure A.9.3.5(b) is a sample sway brace calc.
at the bottom it says "Maximum Fpw per 9.3.5.5.2 (if applicable)."

My question is--
 are those max load tables based on lateral brace spacing ever NOT applicable?

thanks,
Brad


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to