In our jurisdiction the backflow would be required where it enters the building 
from underground.

A long run of black steel pipe is not allowed without a BFP assembly.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, December 06, 2017 3:05 PM
To: [email protected]
Subject: High-Rise with Secondary Water Supply



I’m working on a high-rise that has two water supply lead-ins. One comes in 
adjacent to the pump room, but the secondary supply has to run 200+ feet 
through the building. The plan was to have the backflow preventors in the fire 
pump room. Am I violating any code requirements and/or good design practices by 
doing this? (Note: I know that I’ll need an appropriate distance between the 
backflows and the pump suction and/or to use OS&Y valves).



A couple of potential concerns have been raised:



1.      200-plus feet of “unmonitored” pipe running through the building. I 
guess there is some concern you could have a leak and not have any kind of 
alarm. Is there any code requirement to have a flow switch within a certain 
distance from where the water supply enters the building?

2.      Are there specific code requirements for the pipe type between the 
underground lead-in and the backflow prevention device? We’ve been asked to 
provide galvanized pipe in similar scenarios before, but it was suggested that 
that might not be AWWA-compliant.



Thanks for your input.



Kyle Montgomery

 cid:[email protected]

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

[email protected]







---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to