Todd, can you use figure 8.6.5.1.2(c) to eliminate them? I'm looking at the
2016 edition but I believe that figure goes back to at least 2013 and maybe
2010...


On Wed, Jan 24, 2018 at 6:32 PM Fpdcdesign <[email protected]> wrote:

> There is a 5 ft elevation difference between the ceiling and the bottom of
> the soffit
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
>
>
> Begin forwarded message:
>
> *From: *Kyle.Montgomery <[email protected]>
> *Date: *Jan 24, 2018 at 6:21 PM
> *To: *Sprinklerforum <[email protected]>
> *Subject: RE: [EXTERNAL] Calculation of sprinklers under soffits*
>
> Are you saying that the soffits extend/project 18” from the wall? If so,
> are sprinklers actually required beneath the soffits?
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Fpdcdesign
> *Sent:* Wednesday, January 24, 2018 3:48 PM
> *To:* Sprinklerforum <[email protected]>
> *Subject:* [EXTERNAL] Calculation of sprinklers under soffits
>
>
>
> I have a project where there are existing sprinklers under soffits
> approximately 18" off the wall. The bottom of the soffits is 10 ft and the
> ceiling in the rest of the space is 15 ft. The space is being renovated
> with the high sprinklers being relocated and the sprinklers under the
> soffits remaining. Normally I would include the sprinklers under the
> soffits as part of the hydraulic calculation, but based on the pipe sizes
> (and the preliminary calcs), I don't think they were in the original
> design. Is there any basis for omitting the lower sprinklers by considering
> them as being beneath an obstruction?
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-553-3553 (fax)
>
> 860-608-4559 (cell)
> _______________________________________________ Sprinklerforum mailing
> list [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 