I have always installed FDC's on the discharge side of fire pumps. Looking through 2013 NFPA 20, I don't see anything precluding the instillation on the supply side. Is the FDC allowed to be installed on the supply? I have a contractor that has installed the FDC on the supply run-in, instead of stubing up a secondary line from the remote FDC. Thanks, Jamie