Assuming the stairwell landings are designed large enough from the start, I’d 
put this as preferred location.

-I’ve never seen anyone cut, weld, or use a mechanical hanger to attach some 
third system to a standpipe in a stairwell.

-The entire system is easily seen for inspection. 

-Not much happens in the stairwells. No one leans a ladder against them
accessing a HVAC filter, or bumps them with a scissor lift during a T/I.

-No one messes with any seismic supports because they’re in the way.

Two downsides.

- Various low volt cable sometimes is run parallel to pipe. Pipe and landing 
sleeves make a alluring pathway to some poor guy trying to pull fiber optic to 
the seventh floor.

-I’m not sure how convenient it would be to replace a section if that was ever 
necessary. But that might be true in other installation as well. 


Best.

Bruce Verhei 

> On Feb 2, 2018, at 07:30, Matt Grise <m...@afpsprink.com> wrote:
> 
> That’s a question for  your local building official.
>  
> The code section you are looking for specifically exempts sprinkler piping… 
> depending on how  you read it. Some around here say “no way”. Others don’t 
> mind.
>  
> Matt
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of James Litvak
> Sent: Friday, February 02, 2018 9:24 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Dry Riser in Stairwell
>  
> Can a dry riser be installed in a stairwell, provided there are no clearance 
> issues? I know there is a building code section that doesn't allow any 
> systems in a stairwell that don't serve the stairwell, but I don't know the 
> exact section to check the language. The way I'm looking at it, a dry riser 
> is the same as a floor control assembly, as they are both system risers. 
> Therefore it shouldn't be a problem. However it's being questioned by a 
> building code official. Is this allowed? 
>  
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to