I guess a pdf in a Dropbox is not even really necessary.
What I learned from actually doing the modeling is that a skylight turns otherwise unobstructed construction into obstructed when the sprinkler is directly below it-- like Pete cited ~below the main ceiling like the skylight wasn't there~ And like Roland says about the depth being irrelevant, at 6" deflector with a 155 QR, 12" depth vs 48" is 1 sec activation time dif (so that's 18 vs 54 inch deflector).
How can that be?
Like Roland said, it's all about how much of the plume (ceiling jet) is NOT captured.
Skylights create a kind of upside down obstructed construction!

Brad


Quoting [email protected]:

Hi Forum.
Prompted by the recent deflector distance in skylight thread and what I said about what Roland said about it and after about three weeks doing nothing other than imagining what happens -- I did some modeling on it. Ron G made me aware of the modeling ~5 years ago and at that time some key words in a Goolge search put it on page one. But now it seems Roland's modelling is lost somewhere in the R.O.C. (Republic of China) and you have to sign in to get it.
No way I'm doing that so I did some modeling of my own.

I'll make a pdf and put it in Dropbox by mid next week if there is any intrest but I can tell you: when it comes to a mix of obstructed, unobstructed, and the presence of skylights/small pockets, 9" deflector is the sweet spot.

Thanks,
Brad

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________